Pool pump motor
#1
Pool pump motor
Hi All, 2 HP pool pump motor on a Sta Rite Max E Pro had a blown starting capacitor,pump would run for about 5 seconds and trip the breaker,I replaced the capacitor and nothing changed,runs for about 5 seconds and trips the breaker.
Thoughts
Geo
Thoughts
Geo
#2
Is it getting up to speed before tripping or is it struggling to start? If struggling to start I would check the little contacts that engage/disengage centrifugally when you switch on. Just had to clean the contacts on my table saw motor yesterday. Thought maybe I had a bad capacitor, but after pulling a piece of emery cloth through the contact points, it spins right up.

#3
I removed your other post in the pool section. We'll concentrate on this one.
I agree.... it does sound like the centrifugal starter switch is not releasing.
I agree.... it does sound like the centrifugal starter switch is not releasing.
#6
I was given the wrong info,it trips the GFCI, they said it trips in about 5 seconds and I thought that was a bit quick unless there was a direct short.
Geo
Geo
#7
Is that a combination GFCI breaker ?
If it were a ground fault issue it would probably trip instantly. I'm still going with an overload from the motor start circuit.
If it were a ground fault issue it would probably trip instantly. I'm still going with an overload from the motor start circuit.
#9
I don't know what a combination GFCI is either.
AFCI yes, GFCI no.
GFCI does not trip on a hot to neutral short, only on a ground fault. I would start by swapping out the GFCI. I had a service call about a tripping GFCI on a microwave similar to what you are experiencing and a new GFCI fixed the issue.

I thought that was a bit quick unless there was a direct short
Last edited by Tolyn Ironhand; 01-26-15 at 04:11 PM.