any preferences on wiring hub and spoke vs chaining when running outlets?
are both accepted methods by NEC?
depending on the rout sometimes hub and spoke makes more sense to avoid unnecessary wire overlap
thanks for the opinions
Old 02-02-15, 01:34 PM
Received 1,262 Upvotes on 1,203 Posts
Chaining makes sense when the walls are open but once they're closed it can be better one way one time and another the next.
Old 02-02-15, 01:38 PM
Received 3,898 Upvotes on 3,494 Posts
Both methods are accepted but a good reason to daisy chain them is you end up with two cables in the box.... in and out. Two cables in a standard box are comfortable to work with. Three cables start pushing the spare room.
Old 02-02-15, 02:43 PM
pcboss's Avatar
Received 194 Upvotes on 170 Posts
Both are accepted trade practice and are allowed by code as long as the junction box remain accessible. The daisy chain method is more common.
Old 02-04-15, 04:53 PM
D
Thanks
My application would involve a junction box with 4 wires(1feed and 3 supply)
So I understand the potential issue of clutter. I was thinking of a 4 11/16" box or a standard 4" box with an extender. Are extenders acceptable for use as a splice box?
Old 02-04-15, 04:57 PM
pcboss's Avatar
Extension boxes are fine to added needed box volume. Make sure the conductors extend 3" past the opening.