New Range Hood in old home

After removing an old range hood, there are two wires exposed (black and white). The new range hood has a green ground wire, plus the other two. What should I do with the green wire? Is there another way to ground the range hood?
 
Sponsored Links
  #2  
Old 02-07-15, 07:12 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,365
Do the wires coming from the wall have a spiral metal sheath? If not can you describe the wiring from the wall?
 
  #3  
Old 02-07-15, 07:24 PM
Member
Thread Starter
Join Date: Feb 2015
Posts: 5
No, the wires coming from the wall don't have a spiral metal sheath. The black and white wires appear to be encased in an old material, fabric-like.
 
  #4  
Old 02-07-15, 07:30 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,365
In that case you range hood will not be grounded. The ground would just tuck into the junction box and not be connected.
 
  #5  
Old 02-07-15, 07:39 PM
Member
Thread Starter
Join Date: Feb 2015
Posts: 5
Can we ground the green wire to a screw in the cabinet (which is near the wiring)? We would like it to be grounded if possible.
 
  #6  
Old 02-07-15, 07:51 PM
Member
Thread Starter
Join Date: Feb 2015
Posts: 5
Or is there any way to ground the hood with the existing wires?
 
  #7  
Old 02-07-15, 08:06 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,676
is there any way to ground the hood with the existing wires?
No. New cable or at least add a ground wire all the way back to the main ground in the panel.
 
  #8  
Old 02-07-15, 08:12 PM
Member
Thread Starter
Join Date: Feb 2015
Posts: 5
Thanks you. We appreciate the help.
 
  #9  
Old 02-07-15, 08:13 PM
Handyone's Avatar
Forum Topic Moderator
Join Date: Aug 2000
Location: U.S.
Posts: 5,451
You have no ground available. The screw in cabinet will do no good.

If you have a multimeter, and a gas range, you can check the receptacle behind range for a ground.
A new cable could be pulled up from range receptacle.
 
  #10  
Old 02-07-15, 08:16 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,676
you can check the receptacle behind range for a ground.
A new cable could be pulled up from range receptacle.
If it is part of a dedicated SABC (Small Appliance Branch Circuit) that would be a code violation. However if the home is older there may not be a dedicated SABC.
 