250 volts to 220 volts
#1
Member
Thread Starter
Join Date: Feb 2015
Location: Florida
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
250 volts to 220 volts
Hello,
for our company, we just purchased an industrial CNC machine built in China. We had it built for 220 volts, 2 phase, as we were told that is what we have in our warehouse. Now, when we got it and adjusted all the plugs to fit US sockets, we found out the the voltage in the sockets are from 242v - 249v (mostly in the evening). We contacted the manufacturer and he confirmed that machine should not have problems with 240 volts, but it would be better to keep it lower than that. So 249v might be a big problem for us.
Is there some easy transformer solution to step down from 240-250 to 220 volts?
Thank you very much, please be aware that I do not know much about electricity, volts amps etc
)
for our company, we just purchased an industrial CNC machine built in China. We had it built for 220 volts, 2 phase, as we were told that is what we have in our warehouse. Now, when we got it and adjusted all the plugs to fit US sockets, we found out the the voltage in the sockets are from 242v - 249v (mostly in the evening). We contacted the manufacturer and he confirmed that machine should not have problems with 240 volts, but it would be better to keep it lower than that. So 249v might be a big problem for us.
Is there some easy transformer solution to step down from 240-250 to 220 volts?
Thank you very much, please be aware that I do not know much about electricity, volts amps etc

#3
Anyone ever heard of two phase? (A real question from a non electrician)
Single and three phase is the norm.
Far more common to see three phase in an industrial setting.
Any reason you have not contacted a real local electrician?
Single and three phase is the norm.
Far more common to see three phase in an industrial setting.
Any reason you have not contacted a real local electrician?
#4
I would talk to the manufacturer again. Whoever built this machine (even in China) knows the U.S. runs on 240V.
I seriously doubt if they would send you an expensive machine based on 220 only.
Many people in the U.S. learned to call electric 110/220 way back. It's still called that to many and they are corrected here every day.
I seriously doubt if they would send you an expensive machine based on 220 only.
Many people in the U.S. learned to call electric 110/220 way back. It's still called that to many and they are corrected here every day.
#6
Member
Thread Starter
Join Date: Feb 2015
Location: Florida
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
It is a 2 phase (2 hots). I know there is no 220v in US now, it just confused me when everyone talked about 220ty and it's actually 240ty.
Handyone: Well they said, it can handle 240 volts, but today I measured 249 volts in the socket.
Is there a easy way how to decrease the volts or is it for major wiring upgrade?
Handyone: Well they said, it can handle 240 volts, but today I measured 249 volts in the socket.
Is there a easy way how to decrease the volts or is it for major wiring upgrade?
#8
Single phase 240 volts requires no neutral, unless there are electronics or clocks in the device. It is single phase, not two phase. The voltage can be tweaked by the POCO, but 9 volts is not a deal breaker on the machinery.
#12
We had it built for 220 volts, 2 phase, as we were told that is what we have in our warehouse.
2 hots doesn't mean 2 phase. It would have to be single phase or 3-phase. You need to get someone qualified in there to tell you exactly what you have and to compare it to the machine specifications before you make another very expensive mistake.
The 2 hots you measured could also be from a 3-phase delta service.
Last edited by stickshift; 02-20-15 at 02:52 PM. Reason: corrected typo
#13
Member
Thread Starter
Join Date: Feb 2015
Location: Florida
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
dono
well it has four 2phase vacuum motors, I believe it would not turn them if it was just single phase, right?
it is 50/60hz
so how hard is to get it to 220v, what is needed, is that a major upgrade and what would be the approx costs?
it is 50/60hz
so how hard is to get it to 220v, what is needed, is that a major upgrade and what would be the approx costs?
#14
Babajaga..... you NEED to get an electrician in there. Two phase power is very rare and just about extinct.
Your equipment can also not be 50hz or 60 hz...... it's one or the other and it does make a difference.
99.99% of equipment runs on single or three phase.
Your equipment can also not be 50hz or 60 hz...... it's one or the other and it does make a difference.
99.99% of equipment runs on single or three phase.
#18
We had it built for 220 volts, 2 phase
#19
Voltage is nominal, kind of like a 2x4. In most cases when a voltage is specced on a nameplate, or by a manufacture, it will be +/-10%. So the manufacture says 240 volts is OK, your 249 volts will be just fine. Voltage will go up and down depending load and time of day in your building. If you really want you can buck the voltage down with a buck/boost transformer, however it is likely unnecessary.
I have wired some equipment that was marked "two phase". In each case what they (the over seas manufacture) meant was two hots, and perhaps a neutral, if required. This can be from a single phase service (one coil in a transformer) or two hots of a three phase service (3 coils) Just make sure that if you have a high leg service and the the CNC requires a neutral that you do not use one of the high legs. You will smoke your CNC for sure.
Side note: I have seen many pieces of equipment that are duel rated for 50 or 60 hz power.
Lastly if this is a commercial installation this will likely be required to be wired by a licensed electrical contractor.
I have wired some equipment that was marked "two phase". In each case what they (the over seas manufacture) meant was two hots, and perhaps a neutral, if required. This can be from a single phase service (one coil in a transformer) or two hots of a three phase service (3 coils) Just make sure that if you have a high leg service and the the CNC requires a neutral that you do not use one of the high legs. You will smoke your CNC for sure.
Side note: I have seen many pieces of equipment that are duel rated for 50 or 60 hz power.
Lastly if this is a commercial installation this will likely be required to be wired by a licensed electrical contractor.
#21
Forum Topic Moderator
Can one of the electricians confirm whether a slight over-voltage ~10-15% on motors is typically a bad thing? Assuming the electronics have switching/regulating power supplies, would the over-voltage typically affect the long-term reliability of the motors?
#23
Member
So you talked with the manufacturer and they said that it was OK with 240 volts. Why not talk with them again and ask if there are any issues with 249 volts?
#24
And while talking to them ask them if they really specially built it or if they just pulled a standard unit off the shelf. If standard what countries was intended to be used in?
#25
Member
Thread Starter
Join Date: Feb 2015
Location: Florida
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
2phase
OK I just talked to electrician, he says in US you call it 220 single phase, although it is called 2 phase anywhere else in the world. He also suggested to buy some step down transformer. Can you guys recommend one? It should be 250 to 220v and at least 50 amps
#26
Electrician is wrong on at least two things. Single phase is called single phase or maybe split phase regardless of the country. A knowledgeable person does not call it 220 volts. Actually it would be a buck bost transformer. I'd call the manufacturer first then get a better educated electrician. Bottom line you can probably just plug it in. No rewiring or transformer required.
#27
I imagine you talked to an electrician in China? Since he said "in US you call it 220 single phase, although it is called 2 phase anywhere else in the world".
#28
Hopefully this was not an expensive mistake and is just a lack of knowledge and correct terminology.
#30
A knowledgeable person does not call it 220 volts.
Ray is correct. If you wanted to drop the voltage all you need is a buck boost transformer, and with a single phase load you only need one. Although IMO I doubt you do need one, but if the manufacture says you need to drop the voltage, it would be best to do so to preserve the warranty.
Here is a calculator to size a buck/boost transformer: Buck and Boost Transformer Calculator - Schneider Electric United States
#31
We still haven't cleared up if it is 50hz or 60hz.
Which indicates it was not built for North America. That makes it questionable if it is 60hz. If there are any motors that could be a serious problem.
adjusted all the plugs to fit US sockets,
#32
The real fault is the manufacturer. He should have told you the specs you gave him were wrong for the U.S. 2-phase should have been a red flag even if 220v wasn't. Assuming it wasn't made for the U.S.I'd go back to the manufacturer. Maybe we will let you swap it for one made for the U.S.
#34
I would say there's a good 98% chance that this CNC machine will work just fine in your warehouse. In the US voltages between 220 and 250 all refer to the same thing. I would be really surprised if this machine was designed to operate in such a tight tolerance around 220V instead of simply being built out of commodity parts which are designed to operate in the 220-250 range. You are also likely measuring the voltage on the service with no loads attached. When the motor(s) kick on, the voltage will probably come down to right around 240V. The power company intentionally sets it a little high to compensate for the drop when the load kicks on.
From a practical point of view there really isn't any such thing as two phase, and whomever built this CNC machine wouldn't have any source of motors, controllers and sensors to deal with such a beast. It is much more likely they assumed you meant a standard single phase 240V North American service and built the CNC as such.
From a practical point of view there really isn't any such thing as two phase, and whomever built this CNC machine wouldn't have any source of motors, controllers and sensors to deal with such a beast. It is much more likely they assumed you meant a standard single phase 240V North American service and built the CNC as such.
#36
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
I'm guessing that I am the only one left here that has actually worked with two-phase systems. Two-phase is either FOUR hot wires or four hot wires plus a neutral in the case of a dual voltage system.
If this piece of machinery has TWO hot wires then it is single phase. If it has three hot wires then it is three phase. Either single or three phase MAY have a neutral wire IF the machine requires dual voltage but that is highly unlikely. There should always be an equipment grounding wire.
If this piece of machinery has TWO hot wires then it is single phase. If it has three hot wires then it is three phase. Either single or three phase MAY have a neutral wire IF the machine requires dual voltage but that is highly unlikely. There should always be an equipment grounding wire.
#38
Member
Thread Starter
Join Date: Feb 2015
Location: Florida
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
what transformer type should I use? machine is 7000w, uses around 42 amps (50amp breaker)
could it be this one or what parameters should I look for?
Acme T 1 81048 100 VA Buck Boost Transformer 100 Watt New | eBay
could it be this one or what parameters should I look for?
Acme T 1 81048 100 VA Buck Boost Transformer 100 Watt New | eBay
#39
You really need to contact the manufacturer to clarify the items that have already been asked. The transformer might not even be needed.
#40
Group Moderator
FWIW, I think a machine consistently drawing 42 amps would need to be on a 60 amp breaker.
Pros - am I wrong?
Pros - am I wrong?