Relocating water heater electric

I have a 40 gal electric water heater that I want to move from the center (outside access) of the house to the garage. It will be about a 20' move but with ups and downs maybe 30' additional wire. Currently there is an junction box in the wall near the WH and wiring in flex extend from there to the WH. I'm thinking of extending wires from the existing junction box, tying in with wire nuts, and running up inside the wall, across the attic to the garage to another junction box in the new location. Is a splice like that ok? Otherwise my other choice is to run a whole new length from the circuit breaker which is longer, more expensive and harder.

Your advise is greatly appreciated.

Don
 
Sponsored Links
  #2  
Old 03-06-15, 05:21 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Yes, assuming #10 and a 30 amp dedicated circuit. The white wire will need to be remarked black or red (or any color but gray or green) on both ends using bands of tape or felt tip marker.
 
  #3  
Old 03-06-15, 05:38 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,943
Received 30 Votes on 26 Posts
No need for a second junction box if the WH will be within sight of the panel. If not the cable can end at the required disconnect and then extend over to the WH.
 
  #4  
Old 03-06-15, 06:54 PM
Banned. Rule And/Or Policy Violation
Join Date: Apr 2013
Location: USA
Posts: 4,297
Received 0 Votes on 0 Posts
Keep in mind the further away from the fixtures the longer the water will have to run to get hot.
 
  #5  
Old 03-06-15, 07:50 PM
Member
Thread Starter
Join Date: Mar 2015
Location: USA
Posts: 2
Received 0 Votes on 0 Posts
It's a small house. I added a garage a few years ago and want to reclaim the space the WH is using. The extra water pipe distance is the price I'll pay but it's not all that much.

Thank you all for your replies.
 
  #6  
Old 03-07-15, 06:38 AM
Member
Join Date: Feb 2006
Location: USA
Posts: 6,569
Received 4 Votes on 4 Posts
Junction Box

The junction box where you will make the splice needs to remain accessible.
 
  #7  
Old 03-07-15, 08:13 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Location: USA
Posts: 4,025
Received 18 Votes on 18 Posts
Make sure you insulate the pipes,although it may not be needed as much in Cal. As in the NE.
Geo
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: