Extending a switch loop from a new work box

As I mentioned in a previous thread, I have a light switch that controls a light fixture on the other side of a shared wall. The lower drywall has been removed from both sides of this stud wall As I mentioned in a previous thread, I have a light switch that controls a light fixture on the other side of a shared wall. The lower 2-3 ft of drywall has been removed from both sides of this stud wall as part of mold remediation. I'd like to extend the switch loop coming down from the ceiling fixture through holes drilled in the studs and cut in a new switchbox on the other side of the wall by the doorway.

The switch loop is 12-2 NM w/G. It's held in what appears to be a plastic nail-on 1-gang new work box.

I can try to fish another NM cable through the bottom tab and staple the wire as close as I can to the box about where it emerges below the remaining drywall or as far as I can stick my hand and romex stapler into the stud bay.

My only concern is the rule that that the tabs on single-gang NM new work boxes aren't considered proper cable clamps, hence the rule requiring NM cables be secured within 8” of a 1-gang NM box versus 12” for everything else. I know a lot of rules regarding securing wiring are not applies when the wall is finished as the rules are meant to protect cable during drywall installation. Does this rule still apply and should i then remove the new work box and replace with an old work box? I have an extra Madison SmartBox on hand that I could screw to the existing stud.

If needed I can post pics tonight.

The above assumes the inspector lets me get away with not having a neutral in the switch box as required post-2011.
 
  #2  
Old 03-09-15, 01:41 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
For fished wiring through finished parts of the wall you only need to fasten the NM where you can reach it. If the wire is too loose it couldn't hurt to remove the basic 1 gang box and replace it with an old-work or an Arlington which have better integral clamps.
 
  #3  
Old 03-10-15, 07:04 AM
E
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 38
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks. I'll see if I can push a cable down through the back bottom tab otherwise, I'll cut the box out and hope I can pull the existing cable back into the new box through the box clamp.
 
 