240v surge protector for mini split

Reply

  #1  
Old 03-13-15, 12:24 PM
A
Member
Thread Starter
Join Date: Mar 2014
Posts: 571
Received 23 Votes on 22 Posts
240v surge protector for mini split

Duckless mini split VMH 09/12/18/24 SD
Surge protector 5-2-1 SD 60
240v installation

When hooking up surge suppressor I place leads in circuit breaker and also conductors in breaker correct. No place on suppressor to put conductors going to the outside unit disconnect
Thnx
 
  #2  
Old 03-13-15, 03:53 PM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,649
Received 48 Votes on 43 Posts
No. Surge should go to its own two pole breaker.
 
  #3  
Old 03-13-15, 05:32 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Location: United States
Posts: 4,956
Received 88 Votes on 83 Posts
Although it maybe best to be on it's own breaker I have seen many doubled up on 2 pole breakers as long as the terminals on the breakers are rated for 2 conductors,is this your suppressor ?
Hard Start|Hard Start Kit|Start Capacitor|Compressor for air Conditioning|Start Assist|5-2-1 Compressor Saver|5-2-1|521
Geo
 
  #4  
Old 03-13-15, 06:45 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 60,786
Received 1,324 Votes on 1,224 Posts
The installation for your protection devices states that a 2P20A breaker be used.
 
  #5  
Old 03-14-15, 08:07 AM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,283
Received 109 Votes on 101 Posts
Some surge protectors do not have separate "line" terminals to connect to a feed line or a breaker and "load" terminals to connect the air conditioner unit or other device or electronics to be protected. These surge protectors may be connected anywhere in the house electrical system provided they have proper overcurrent protection as their instructions specify.
 
  #6  
Old 03-14-15, 09:32 AM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 36 Votes on 28 Posts
What do ducks, or a lack of ducks, (duckless) have to do with anything?
 
  #7  
Old 03-14-15, 07:54 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,754
Received 97 Votes on 87 Posts
What do ducks, or a lack of ducks, (duckless) have to do with anything?
I was wondering the same thing. All I can think of is the mini-split will be quackless.
 
  #8  
Old 03-15-15, 06:59 AM
A
Member
Thread Starter
Join Date: Mar 2014
Posts: 571
Received 23 Votes on 22 Posts
Thank you everyone. Will use a dedicated 2 pole 20amp breaker for this.
Thanks
 
  #9  
Old 03-15-15, 09:12 AM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,283
Received 109 Votes on 101 Posts
Duckless -- Has no components for which duck tape is commonly used to hold together or aid in the installation.

OT: Other cavalier use by me of trademarks: "... romex cable of the same gauge works just as well for audio as monster cable or oxygenated cable although it might not be as attractive looking ...
 
Attached Images  

Last edited by AllanJ; 03-15-15 at 09:33 AM.
 