Wall Heater Installation in Bathroom

I want to install an electric wall heater in my bathroom. It is 240V, 1300 watts, 5.42 amps.

What sort of wire would I need? Can I use 14/2 or 14/3?

Do I need a GFCI breaker since it is located in a bathroom?
 
  #2  
Old 03-14-15, 01:32 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,639
Received 3,892 Upvotes on 3,489 Posts
Welcome to the forums.

You would use 14-2 w/ground as you don't require a neutral.
A GFI breaker is not required by code if that is a hard wired heater. However, the manufacturer could specify GFI protection if used in a wet location like a bathroom. You'd need to check the installation instructions.

Personally, I'd install a GFI breaker.
 
  #3  
Old 03-14-15, 05:28 PM
D
Member
Thread Starter
Join Date: Mar 2015
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Installation instructions say nothing about a GFI breaker, but like you, I think I'll install one anyway.
 
  #4  
Old 03-14-15, 06:07 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,970
Received 194 Upvotes on 170 Posts
GFI protection not required, nor would I waste money on an expensive GFI breaker. The heater is not being constantly touched. Mine even has a plastic trim housing.
 
  #5  
Old 03-14-15, 08:11 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,639
Received 3,892 Upvotes on 3,489 Posts
I have to disagree.... I don't consider spending money on a GFI breaker in this case as a waste of money.
 
 