Cable securing - Horizontal through studs and multiple gang plastic boxes

Question 1 - Is cabling secured making a long (25') run horizontally through studs?

Meaning, through holes I'm about to drill in the studs. Code says to fasten every 4.5 feet to a surface over which it runs. Since I'm more running "through" surfaces rather than "over" them, I'm confused whether this means to fasten during the 25' run or not.

I know it has to be secured once it starts moving vertically over the studs. (Down from the panel, down to the outlet box.)

Question 2 - Code says when using a single gang plastic box, the cable doesn't have to be anchored if it is supported within 8" of the box and at least 1/4" of the sheath extends into the box. What do I do with two gang plastic boxes? Have I overlooked a cable clamp meant for plastic boxes?
 
Sponsored Links
  #2  
Old 03-20-15, 03:37 PM
Group Moderator
Join Date: Oct 2004
Location: WI/MN
Posts: 19,369
Received 54 Votes on 51 Posts
Welcome to the forums.

1. No
2. Sorry, not sure I'm understanding this one - can you explain?
 
  #3  
Old 03-20-15, 03:52 PM
Handyone's Avatar
Member
Join Date: Aug 2000
Location: U.S.
Posts: 5,451
Received 0 Votes on 0 Posts
The remodel plastic boxes have integrated clamps. You need to punch it out a little to break the factory nibs, but after that you can push a cable through and it will hold.

If using new work boxes, the knockout will offer no strain relief. The staple within 8" is sufficient.

Technically, when remodeling and using "old work" boxes, no securing (stapling) of cable is required for the inaccessible parts of the run.
 

Last edited by pcboss; 03-20-15 at 06:10 PM. Reason: technical correction
  #4  
Old 03-20-15, 06:08 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,957
Received 33 Votes on 28 Posts
Device boxes larger than single gang have clamps for the cables. The cables for those need to be secured within 12".
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: