Running direct burial wire through conduit
#1
Running direct burial wire through conduit
Is there a trick to simplify running Direct Burial Wire through PVC conduit? I'm wiring a sub panel to a detached garage and I'll be installing the conduit a I wire it. Should I run the wire through the PVC as I go or should I install all the conduit then pull the wire? I'm running 4/3 w/ Ground so 4-4 Guage wires wrapped in one insulation. Thanks for any ideas...
#2
Group Moderator
It sounds like you're running cable in conduit and you can't do that - needs to be individual wires like THWN.
Can you clarify?
Can you clarify?
#3
I'm running 4/3 w/ Ground so 4-4 Guage wires wrapped in one insulation.
#5
I am wiring a sub panel in a detached garage. The Main Panel in the house is 150 Amp, I'm installing a 60 Amp double pole breaker in the main panel. The sub panel will have a 60 Amp Main Breaker and 2-15 Amp & 2-20 Amp breakers. As for the feeder line, I was planning on "Double Protecting" myself by running direct burial cable inside conduit. My concern is exactly what you guys are saying, it's hard as heck to do that. I just wired my own basement w/ 14/2 w/ ground (about 300 ft of wire) and some of it was crazy to pull through floor joists. So, I'm assuming running 4/3 with Ground is virtually impossible. So, should I be running 4-single wire through the conduit? Is that enough protection? My run is approx. 30 feet (underground) and my concern is not the straight conduit, it's the entrance into the garage which is a 90 degree fitting....
#7
I'm running 4/3 w/ Ground so 4-4 Guage wires wrapped in one insulation.
So, should I be running 4-single wire through the conduit? Is that enough protection?
Yes and Yes. That is the usual way and provides the necessary protection.

#8
So when running the individual cables (#4 red, black, white, green), how should it be run from the main panel box to where it exits the house? It will run approx. 30 feet inside the house from the main panel to the exit to the outside conduit. does it have to e in conduit inside the house?
#12
Thanks Furd, I thought I had this all figured out, but... I calld the local electrical supply shops looking for 4-#4 copper THWN Wires (1 Green, 1 White, 1 Black, 1 Red) assuming 1 neutral, 1 ground, 2 hot and none of them had #4 THWN in any color except black. Am I looking for the wrong stuff? I'm running a 60 Amp Breaker in the Main Panel, then a 60 Amp Sub panel 100 feet away in a detached garage. Is the 4 - #4 single THWN conductors run in conduit not the correct gauge? Should I be using #6 conductors?
#13
Non white wires #6 and smaller can not be redesignated as neutral. #4 can be so often just black is used. You need to put bands of white tape on both ends. No need to mark one black red. You can have two blacks. You only need #8 for ground and that should be available in green.
#14
Thanks Ray2047, so I can use 2- Black #4 (Hots), 1- Green #8 (Ground), and you're saying to use 1- Black #4 (Neutral) and color the ends white, correct? Does that pass code?