What gauge wire do I need for 240 volt 50 amp also will this breaker box work.
#1
Member
Thread Starter
Join Date: Nov 2012
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
What gauge wire do I need for 240 volt 50 amp also will this breaker box work.

I want to run a dedicated line to garage for 220 volts on 50 amp breaker. This is for a stick welder. What gauge wire do I need? Which wire hooks up where?? Breaker and receptacle. And then I have picture of my breaker box. Will it work with 50 amp breaker on lower left side? Thanks in advance
Dean
#2
If it is a detached garage and you have lights and receptacles the feed for that will need to be abandoned and a subpanel installed at the garage. You can only have one feed to a detached structure.
#4
6-2 NM-b on a 50 amp breaker.
(Note the NEC has special rules for welders based on duty rating that might allow smaller cable and/or beaker but going with 6-2/50a breaker is good future proofing.)
(Note the NEC has special rules for welders based on duty rating that might allow smaller cable and/or beaker but going with 6-2/50a breaker is good future proofing.)
#5
Member
Thread Starter
Join Date: Nov 2012
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I just learned about duty ratings and understand what you're saying... and agree if you're going to go to the trouble to install a new line/outlet...you may as well make it to handle anything down the road. Thanks!! Off to get my wire/breaker/receptacle...