outside wire

Reply

  #1  
Old 03-25-15, 05:44 PM
Member
Thread Starter
Join Date: Jun 2005
Location: ontario canada
Posts: 381
outside wire

I need to run an outdoor cable for an outdoor wood stove power supply. it is a short run of about 50 feet, I have enough direct burial 14/2 but I would like to go out through the cement foundation above grade. Would it be alright to use a short piece of steel or plastic conduit (about 24 inches) to protect the wire that would be seen on the outside foundation wall?
 
Sponsored Links
  #2  
Old 03-25-15, 09:30 PM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,356
The cable is type UF, not "outdoor cable".

Not only is it acceptable to use conduit for protection it is REQUIRED. Use an LB fitting to turn the hole in the house downward and then a piece of PVC conduit down to the burial depth and with a 90[SUP]o[/SUP] bend to bring it back horizontal.

Also, foundations are made with concrete, not cement.
 
  #3  
Old 03-26-15, 03:38 PM
Member
Thread Starter
Join Date: Jun 2005
Location: ontario canada
Posts: 381
thanks for the information on the conduit. And I will try and remember to use the proper terminology for the gravel/cement mixture (concrete) and the direct burial outdoor electric cable (UF-B direct burial) from here forward
 
  #4  
Old 03-27-15, 06:56 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,295
Billie, I believe the cable designation in Canada is NMWU instead of UF-B. Basically the same stuff but you might have trouble finding cable marked with "UF" in Canada.
 