GFI required?

My son just bought an older home built in in 1981 in Orlando, Fl. I went through every circuit to correct any "abnormalities" or improper wiring details. I am unclear on one point.

As I understand it, any outlet in a garage should be GFI protected and there is the one that also leads to the two bathrooms for those outlets. Yet, there is a dedicated 20 amp. circuit with a regular outlet that serves just the washing machine, but this is in the garage itself. Should I upgrade the outlet to a 20 amp. GFI? Does the code now require this? Just want to do things the right way. Thanks!
 
  #2  
Old 03-26-15, 12:21 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
Current code requires all 120V receptacles in a garage to be GFCI protected regardless of purpose. There is also a requirement that the laundry receptacle(s) be GFCI protected no matter where the laundry area is in the house. You do not need to use an actual 20A (t-slot) receptacle as 15A receptacles are allowed on general purpose circuits because they have a 20A pass-thru rating.
 
  #3  
Old 03-26-15, 12:51 PM
S
Group Moderator
Join Date: Oct 2004
Location: WI/MN
Posts: 19,180
Received 1,278 Upvotes on 1,217 Posts
Ben - I thought you could put 15 amp receptacles on a 20 amp circuit only if there were two or more receptacles on the circuit. Am I mistaken about that?
 
  #4  
Old 03-26-15, 12:55 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
Yes that's correct, but a standard duplex GFCI receptacle counts as 2 outlets.
 
  #5  
Old 03-26-15, 01:21 PM
S
Group Moderator
Join Date: Oct 2004
Location: WI/MN
Posts: 19,180
Received 1,278 Upvotes on 1,217 Posts
That makes sense - thank you.
 
  #6  
Old 03-26-15, 01:28 PM
F
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 21
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thank you. I now see I have another task. My other son's house has the laundry room inside the house, and I know there is no GFI. Will upgrade that as well. Of course these houses were in compliance when built, but I view the upgraded code as a safety guide. Things are changed for a reason. I'll heed that.
 
 