Hi guys,

I'm currently renovating my home office and have a question.

The office was previously wired with BX cable (black and white wire wrapped in cloth). There were two wall sconces (with pull chain) and four outlets.

What I want to do is get rid of the BX that is in the room with the exception of the line coming in that feeds the power. Get rid of the two sconces and replace them with a ceiling light with a light switch, and three outlets.

The BX line coming in is too short (it was originally connected to one of the sconces). To get it to the light switch can I use a metal box, feed the BX into that and clamp it, then feed in Romex - ground it to a green screw, and connect the Black/Black and White/White wires together to create an extension?

Here's a picture of what I have so far:
Name:  IMG_20150329_092754.jpg
Views: 11152
Size:  40.4 KB

Also, for the sake of reference here are some diagrams I threw together to illustrate what I'm trying to do:

Old Wiring (all BX)
Name:  old-wiring.jpg
Views: 8485
Size:  18.8 KB

New Wiring (BX power feed, everything else upgraded to Romex)
Name:  new-wiring.jpg
Views: 8363
Size:  18.8 KB

Thoughts?
Thank you!
SB
 
  #2  
Old 03-29-15, 09:50 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,074
Received 161 Upvotes on 147 Posts
Your plan will work however you will have to many conductors in that box,actually you could install a 4" Sq. Box with single device plaster ring ,use a connector rated for MC on top and 2 Romex connectors on the bottom,the circuit will need to be protected by an AFCI device either a breaker or receptacle.
Geo
 
  #3  
Old 03-29-15, 10:24 AM
S
Member
Thread Starter
Join Date: Mar 2015
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks @geochurchi, how do I install a 4" square box in the wall? I was going to use the single gang switch and just put a "blank" cover over it.

Take a look at the following, this is how I translated your reply.

Name:  facing-wall-2.jpg
Views: 9892
Size:  24.0 KB

So the power (BX cable) goes into the junction box. In that I would take romex down to the light switch and then from the switch, run a line to the ceiling light.

Also in the box with the BX cable would be a second run of wire which runs down to the outlet.

Does that look right?
 
  #4  
Old 03-29-15, 10:31 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
How old is the BX? Does it have a bonding strip/wire?

Name:  111ecmCBfig1.jpg
Views: 9661
Size:  25.4 KB
 
  #5  
Old 03-29-15, 10:50 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,929
Received 3,950 Upvotes on 3,543 Posts
Like Geo mentioned you could use a 4" box and ring to do what you need.

Name:  1900combo.jpg
Views: 6619
Size:  26.7 KB
 
  #6  
Old 03-29-15, 11:04 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,074
Received 161 Upvotes on 147 Posts
If you intend to blank off the box then that would work,just change the clamp for BX, also as Ray stated make sure it has the bond strip in the armor otherwise you can not extend that ungrounded circuit.
P/S use the deepest box you can get into the wall
Geo
 
  #7  
Old 03-29-15, 11:20 AM
S
Member
Thread Starter
Join Date: Mar 2015
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Hi @ray2047,

The house was built in 1932 so I think the BX is pretty old. There are remnants of knob and tube through the house as well, so I believe the BX came in at a later date. The cloth is pretty deteriorated at the ends so maybe 50 years old?

Here's a close up of the wire. I don't see anything that would look like a bonding strip. There is a brass/copper colored piece at the end of the cable. Not sure what that is for.

See below:
Name:  IMG_20150329_140947.jpg
Views: 6434
Size:  34.0 KB

Name:  IMG_20150329_141008.jpg
Views: 6857
Size:  27.5 KB
 
  #8  
Old 03-29-15, 12:07 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
I don't see anything that would look like a bonding strip.
That and the picture say it is unlikely your BX provides a reliable ground. Therefore you are going to need to run a new circuit from the breaker box.
 
  #9  
Old 03-29-15, 03:26 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,976
Received 194 Upvotes on 170 Posts
Another thing to consider is the load on the existing circuit that you are adding on to. I would run a new circuit even if the lack of grounding issue was not there.
 
  #10  
Old 04-02-15, 02:40 PM
S
Member
Thread Starter
Join Date: Mar 2015
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks Ray. That's what I was afraid of. Appreciate everyone's help!
 
 