Wire fill for 2 1/2" conduit
#1
Member
Thread Starter
Join Date: May 2012
Posts: 36
Received 0 Votes
on
0 Posts
Wire fill for 2 1/2" conduit
Panel is on outside wall of house. 2 1/2" conduit is about 8" long attached to back of panel going through exterior wall into interior wall cavity. How many 12/2 romex or combination of 12/2 and 14/2 can go through it?
#3
As many as you can cram in there. Conduit fill and derating rules do not apply for pipes less than 24" in length. When you're done it should be sealed with duct seal as this is an interior to exterior run.