Wire fill for 2 1/2" conduit


  #1  
Old 04-03-15, 08:45 AM
M
Member
Thread Starter
Join Date: May 2012
Posts: 32
Upvotes: 0
Received 0 Upvotes on 0 Posts
Wire fill for 2 1/2" conduit

Panel is on outside wall of house. 2 1/2" conduit is about 8" long attached to back of panel going through exterior wall into interior wall cavity. How many 12/2 romex or combination of 12/2 and 14/2 can go through it?
 
  #2  
Old 04-03-15, 09:49 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,057
Received 159 Upvotes on 145 Posts
That is considered a nipple and I don't believe there is an limit,however bundling may be an issue.
Geo
 
  #3  
Old 04-03-15, 09:54 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
As many as you can cram in there. Conduit fill and derating rules do not apply for pipes less than 24" in length. When you're done it should be sealed with duct seal as this is an interior to exterior run.
 
  #4  
Old 04-03-15, 02:51 PM
M
Member
Thread Starter
Join Date: May 2012
Posts: 32
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yes, I do remember when I bought it I had to ask for a nipple.
I do have a lot of 12/2's and a few 14/2's to pass through it. Relieved it won't be a problem. Thank you.
 
 