Adding sub-panel for new second floor
Remodeled house and went from a single story to a two story house. I want to run electricity upstairs. Upstairs will consist of my office (running several computers, a bedroom, and a game room. There isn't a bathroom upstairs.
I need to know some guidelines to determine what size breaker should be used on the main panel to feed a sub-panel on the 2nd floor.
Can I use Romex 8/2 (with 10gauge ground) to feed the sub-panel or do I need 8/3 with ground?
What size breaker should be used in the sub-panel? I plan to buy all the electrical components at Lowes. Any suggest as to name brand to use?
I plan to use 12/2 for internal wiring following the guidelines I've read on other posts and 20amp outlets. What is the recommended number of outlets per run?
Any assistance would be greatly appreciated.
I need to know some guidelines to determine what size breaker should be used on the main panel to feed a sub-panel on the 2nd floor.
Can I use Romex 8/2 (with 10gauge ground) to feed the sub-panel or do I need 8/3 with ground?
What size breaker should be used in the sub-panel? I plan to buy all the electrical components at Lowes. Any suggest as to name brand to use?
I plan to use 12/2 for internal wiring following the guidelines I've read on other posts and 20amp outlets. What is the recommended number of outlets per run?
Any assistance would be greatly appreciated.
#2
I need to know some guidelines to determine what size breaker should be used on the main panel to feed a sub-panel on the 2nd floor.
Can I use Romex 8/2 (with 10gauge ground) to feed the sub-panel or do I need 8/3 with ground?
Can I use Romex 8/2 (with 10gauge ground) to feed the sub-panel or do I need 8/3 with ground?
What size breaker should be used in the sub-panel?
#4
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
Using #8 type NM cable is only going to give you a 40 ampere panel, not even worth the effort in my opinion. I would use nothing less than #6 with a 60 ampere feeder circuit breaker in the service panel.
#5
I would use nothing less than #6 with a 60 ampere feeder circuit breaker in the service panel.
I plan to use 12/2 for internal wiring following the guidelines I've read on other posts and 20amp outlets. What is the recommended number of outlets per run?
#6
Member
Thread Starter
Join Date: Apr 2015
Location: usa
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The electrical guy at Lowes said the same thing about using #6 wire. It's a short run from the main box to the main lug panel (18ft). From there, I'll branch out the circuits. No heavy loads (copy machine, refrigerator, etc upstairs. Game room is for the pool table and fooseball. Only lights and outlets for general use there.
Thanks for all the input. This site is very useful!
Thanks for all the input. This site is very useful!