re-purpose hot tub 240v GFCI - welding 240v outlet - HALP
Old 04-06-15, 05:07 PM
juanjonSF's Avatar
Hey peoples.. new to this forum looking for some HALP!!
I got rid of a hot tub, and bought a welder.. and I'd like to re-use the hot tub wiring and re-purpose for my welding projects.. as my welder can run on 240.
the GFCI is a connecticut electric 50 amp 240 volt SPA disconnect.
http://d163axztg8am2h.cloudfront.net...32542b716e.pdf
wondering.. should I by-pass the GFCI? to prevent tripping?
and it seems this GFCI has an option for a 120V branch circuit.. I'd certainly like to have two 120 outlets in addition to the 240!
how would you go about accomplishing this??
any help is much appreciated!!!
Jon
SF, CAName:  IMG_9810sm.jpg
Old 04-06-15, 05:11 PM
ray2047's Avatar
Received 13 Votes on 11 Posts
What is the input amps on the welder?
Old 04-06-15, 05:25 PM
juanjonSF's Avatar
hey ray.. millermatic 211 so 25 - 30 amps
Old 04-06-15, 05:26 PM
F
Received 36 Votes on 28 Posts
Nice machine! 30% duty cycle so should be no problem whatsoever. You MAY need a different (or additional) circuit breaker installed.
You most certainly can add 120 volt circuits to this BUT they will also detract from the 240 volt maximum power. What size circuit is feeding this panel?
Removing the GFCI would be easy but I don't think there is any advantage in doing so, I could be mistaken.
Old 04-06-15, 05:51 PM
juanjonSF's Avatar
it's a 50amp circuit.. so thinking maybe keeping it wired as is, adding the 120v branch circuit as shown here - http://d163axztg8am2h.cloudfront.net...32542b716e.pdf
and connecting a nema 6-50R outlet to the existing GFCI output, that used to supply (240v) the hot tub..
Old 04-06-15, 11:12 PM
F
Yes, that will work. I would be tempted to remove the contactor as it is not necessary and I might add a 2-pole auxiliary circuit breaker rated at 30 amperes for the welder. Do you have an actual picture of the inside of this panel rather than just a drawing?
Old 04-07-15, 05:38 AM
Geochurchi's Avatar
Received 91 Votes on 86 Posts
Why not leave things as they are currently connected and see how the welder operates.just curious,what controls that contactor,and is that a 250volt GFCI?
Geo
Old 04-13-15, 09:02 PM
juanjonSF's Avatar
update.. all set!
welder running a lot smoother on the 240v 50A circuit! and my extra 120 outlets sure are handy! thanks for the help peoples! Name:  1294252_10153142680366421_1928023447908848894_o.jpg
Old 04-13-15, 09:04 PM
ray2047's Avatar
Thanks for letting us know the outcome.
Old 04-14-15, 01:08 AM
F
Please tell me this is not outside as neither that armored cable nor the 240 volt receptacle are listed for use outside.