How do I make my 110v outlet a 220v outlet
Old 04-06-15, 06:36 PM
Q
I have a 110v outlet for my air conditioner but I need a larger air conditioner which means I will need a 220v 15 amp outlet. I have 12-2 MClite on that circuit. I was told I can use the current neutral wire as a hot and the current hot as the second hot and the current ground wire as the ground since a 220 circuit is 2 hots and a ground. Is there any reason why this would not be advisable?
Old 04-06-15, 06:46 PM
A
Received 279 Upvotes on 255 Posts
First verify that there are no other things (receptacles, lights, etc.) on that circuit.
Then you may re-purpose the cable as a 240 volt circuit, substituting a 15 amp 240 only volt single receptacle in the existing outlet box at the air conditioner..
You will need a double wide double 15 amp breaker with a single handle or two handles tied together to connect the white and black wires of this cable to at the panel.
Mark both ends of the white wire with a band of black tape or stain.
Old 04-07-15, 05:10 AM
Geochurchi's Avatar
Received 161 Upvotes on 147 Posts
If the circuit is indeed 12/2 MC and nothing else is on that circuit,upgrade it to a 20 - 240 volt circuit,same thing applies as AllanJ stated except for a 2 pole 20 amp breaker and a 20 - 250 volt single receptacle.
Go For It!
Geo
Old 04-08-15, 10:00 PM
Q
Yes, I know for sure that is a dedicated line for the air conditioner. Thanks guys for your input.