Conduit ground ?
Is there a problem with extending ground by connecting to metal conduit (that is grounded via the breaker box) using a conduit ground clamp and wire to a receptacle?
#2
The metal box would be grounded by the conduit. You don't need to connect a wire from the conduit to the receptacle, but from the metal box to the receptacle by using a ground screw installed in the metal box or a ground clip attached to the side of the metal box.
#3
Member
Thread Starter
Join Date: Aug 2013
Location: USA
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
To clarify: I failed to pull a gnd wire when I extended my shop circuit ( metal conduit) to a shed.
Therefore I pulled a green wire to the shed & attached it to the receptacle ground.
I connected this gnd wire to the shop conduit & tested the receptacles in the shed with a known working 3 led tester.
The result NO ground.
I'm baffled, I have checked continuity at each conduit connection where gnd could be lost, but they all ohm out ok.
Therefore I pulled a green wire to the shed & attached it to the receptacle ground.
I connected this gnd wire to the shop conduit & tested the receptacles in the shed with a known working 3 led tester.
The result NO ground.
I'm baffled, I have checked continuity at each conduit connection where gnd could be lost, but they all ohm out ok.