Conduit ground ?


  #1  
Old 04-18-15, 07:08 AM
R
Member
Thread Starter
Join Date: Aug 2013
Location: USA
Posts: 7
Upvotes: 0
Received 0 Upvotes on 0 Posts
Conduit ground ?

Is there a problem with extending ground by connecting to metal conduit (that is grounded via the breaker box) using a conduit ground clamp and wire to a receptacle?
 
  #2  
Old 04-18-15, 07:49 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,842
Received 179 Upvotes on 162 Posts
The metal box would be grounded by the conduit. You don't need to connect a wire from the conduit to the receptacle, but from the metal box to the receptacle by using a ground screw installed in the metal box or a ground clip attached to the side of the metal box.
 
  #3  
Old 04-20-15, 07:36 AM
R
Member
Thread Starter
Join Date: Aug 2013
Location: USA
Posts: 7
Upvotes: 0
Received 0 Upvotes on 0 Posts
To clarify: I failed to pull a gnd wire when I extended my shop circuit ( metal conduit) to a shed.
Therefore I pulled a green wire to the shed & attached it to the receptacle ground.
I connected this gnd wire to the shop conduit & tested the receptacles in the shed with a known working 3 led tester.
The result NO ground.
I'm baffled, I have checked continuity at each conduit connection where gnd could be lost, but they all ohm out ok.
 
  #4  
Old 04-20-15, 07:48 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,158
Received 814 Upvotes on 685 Posts
When you say you ran metal conduit to your shed, I hope you ran Rigid conduit if it is buried in the ground. EMT is not listed for direct burial.
 
  #5  
Old 04-20-15, 08:25 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,935
Received 181 Upvotes on 159 Posts
Please post s picture of the ground connection to the conduit.
 
 