Ground bar for multiwire circuit sub panel?

I'm running a multiwire circuit from my main panel to an outdoor shed. On the shed I have a sub panel with two 20 amp breakers. My question is whether I need a ground bar on the sub panel or if I can just tie the ground wires together in the panel? I don't see any factory holes to attach a ground bar.
Name:  20150419_092510_resized.jpg
Views: 821
Size:  29.7 KB
 

Last edited by pschumac; 04-19-15 at 11:15 AM. Reason: adding picture
  #2  
Old 04-19-15, 11:17 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,974
Received 194 Upvotes on 170 Posts
Some brands require holes to be drilled for the ground bars. The panel label should show where to install the bar.
 
  #3  
Old 04-19-15, 12:06 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
For only two 20 amp circuits you don't need a subpanel. Opinion: If you are going to the effort of a subpanel it should be larger. If all you need is two 20 amp, 120v circuits a simple multiwire circuit will do the job and no subpanel or ground rod needed, just a disconnect either one intended for an A/C or a 20a DPST switch.
 
  #4  
Old 04-19-15, 04:05 PM
P
Member
Thread Starter
Join Date: Jan 2008
Location: United States
Posts: 16
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the replies.

The diagram shows that the ground bar goes to the right of the breakers. There doesn't seem to be much room there.

Yes, I only need two 20 amp circuits.so a larger subpanel isn't necessary. Good idea to use an AC disconnect switch. However, since I already have this panel installed, I'd like to make this work. Do I really need to install a ground rod?
 
  #5  
Old 04-19-15, 04:15 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Do I really need to install a ground rod?
Yes, at least one. It needs to be eight feet long by one half inch in diameter minimum driven flush with the ground. Ground wire is usually #6. You can use less thnt #6 but then you would need to protect it with conduit.
 
  #6  
Old 04-19-15, 07:49 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,870
Received 185 Upvotes on 166 Posts
Do I really need to install a ground rod?
It's just a 20 amp multiwire branch circuit. Take out the panel and use the A-C disconnect (about $6.50 at Lowes) and you don't need to add a ground rod/rods.
 
 