Wiring outets and switches in detached garage


  #1  
Old 04-19-15, 11:10 AM
J
Member
Thread Starter
Join Date: May 2007
Location: New York
Posts: 270
Upvotes: 0
Received 1 Upvote on 1 Post
Wiring outets and switches in detached garage

I am wiring outlets in a detached unheated garage. It will be installing drywall. Can I run the romex through the wall studs since it will have drywall?
Also, the lights or the entrance door (man door), can the switch for it be just inside the man door?

Thanks...
 
  #2  
Old 04-19-15, 11:43 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,883
Received 3,750 Upvotes on 3,362 Posts
The wiring thru the wall studs and then covered by sheetrock is fine. The switch for the lights usually goes near the door that gets the most use..... in your case.... the man door.
 
  #3  
Old 04-19-15, 02:17 PM
J
Member
Join Date: Jan 2011
Location: USA
Posts: 4,463
Received 128 Upvotes on 113 Posts
Hole needs to be in the middle of the studs so you do not hit them when screwing up the drywall.
 
  #4  
Old 04-19-15, 07:44 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,842
Received 179 Upvotes on 162 Posts
Also, all receptacles need GFCI protection.
 
  #5  
Old 04-20-15, 03:28 AM
J
Member
Thread Starter
Join Date: May 2007
Location: New York
Posts: 270
Upvotes: 0
Received 1 Upvote on 1 Post
So the GFCI breaker is the way to go?
 
  #6  
Old 04-20-15, 05:54 AM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,454
Upvotes: 0
Received 267 Upvotes on 243 Posts
For a garage subpanel, ground fault circuit interrupters as breakers or as the first receptacle in each daisy chain is your choice.

With no subpanel, and just a 15 or 20 amp 120 only or 120/240 volt) circuit coming from the main house, a GFCI breaker in the main house has the disadvantage that if it trips then you have to walk back to the house to reset it.

(You're not allowed to have more than one circuit bringing power to the garage. If you are just getting started and laying the feed from the main house, we suggest #8 wire for 40 amps or even #6 gauge for 60 amps as futureproofing even if you don't install the garage subpanel yet and limit the circuit to 20 amps. All require separate ground and neutral and, for 240 volts, two hots.)
 
  #7  
Old 04-20-15, 08:08 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,842
Received 179 Upvotes on 162 Posts
So the GFCI breaker is the way to go?
A GFCI receptacle as the first receptacle on each circuit is a lot less expensive than just one GFCI breaker and provides the same protection.
 
 

Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: