Romex in conduit

Can I put 12/2 romex in 15" of 1/2" conduit running from inside wall to the outside?
I am installing an outside light. I can run a 12/2 from the inside and then into 15" of conduit to a box where the exterior light mounts.
 
Sponsored Links
  #2  
Old 04-27-15, 02:00 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Yes, in fact you must use protective conduit if the cable is running through a masonry wall (brick, stucco, etc). The conduit should be sealed with caulk or duct sealant once wire is pulled through. Jurisdictions which are very strict on the code may want you to use UF-B or another type of waterproof wiring method in place of that segment of NM-B which is "dry use" only.
 
  #3  
Old 04-27-15, 03:19 PM
Member
Thread Starter
Join Date: May 2012
Posts: 36
Received 0 Votes on 0 Posts
Thanks. I thought romex, whether NM-B or UF-B in conduit is not permitted due to heat considerations but the short distance might be allowed. I was thinking I might have to run individual conductors.
 
  #4  
Old 04-27-15, 07:11 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,975
Received 35 Votes on 30 Posts
NM in a conduit sleeve inside is fine. NM used outside, even in conduit, is not.
 
  #5  
Old 04-28-15, 11:49 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 8,470
Received 1 Vote on 1 Post
I thought romex, whether NM-B or UF-B in conduit is not permitted due to heat considerations
Romex® is a federally registered trademark owned by Southwire. It refers to their brand of Type NM cable. It is (too) commonly used as a nickname for any and all Type NM cable, but does not refer to any other type of wiring assembly.

That said, you are right. Type NM cable cannot be installed in conduit and be in compliance with the NEC. Pcboss is also right. Running type NM cable through a conduit sleeve for protection is not only fine, it's required.

Confused? Here's the distinction: Type NM cable cannot be installed in place of individual conductors in a closed conduit system. The potential for damage from excessive heat is a primary reason for that prohibition.

"Sleeving" type NM cable involves running it through a (usually) short piece of conduit which is open on both ends, to protect it from physical damage while allowing the heat to escape. I only put a sealant around a sleeve, not in it.

If what you're planning to do is have one end of the conduit attach to the box that the light will be mounted on, then you aren't planning to use a sleeve. That would be an extension of the enclosed mounting box. In that case, the conduit needs to run to a second, interior, closed box. The Type NM should be spliced to individual conductors in the first box, and those should be run to the outside box.
 
middletown0211 voted this post useful.

Last edited by Nashkat1; 04-29-15 at 01:04 AM. Reason: Add hotlink
  #6  
Old 04-30-15, 07:09 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,215
Received 38 Votes on 30 Posts
Type NM cable cannot be installed in conduit and be in compliance with the NEC.
No cable assembly can be installed in a complete and closed conduit system in my area, but I am not aware of the NEC actually prohibiting NM cable from being run in conduit.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: