I am researching a project similar to BDOBS and can use some help. I have 12/2 stubbed to a exterior box. Would like to wire in two switches and pull 12/3 from the switches to an outlet at my pond and be able to control the top of the outlet with one switch and the bottom with the other. If I can't split a GFCI outlet I can install a GFCI breaker if that is the best way to go?

Was hoping someone could provide a diagram of the proper way to wire this up, or at the very least explain it all as I have searched hi and low online for a schematic with no luck.

Thanks in advance
 

Last edited by ray2047; 04-28-15 at 12:28 PM.
  #2  
Old 04-28-15, 10:34 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,976
Received 194 Upvotes on 170 Posts
You just need to supply the gfi protection before the receptacles.
 
  #3  
Old 04-28-15, 11:20 AM
B
Member
Thread Starter
Join Date: Apr 2015
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
I understand the GFCI protection part. What I was hoping for (need) is a picture of the wiring between the two switches and the outlet? 12/2 to the two switches, 12/3 from the switches to the top and bottom of the plug-in.
 
  #4  
Old 04-28-15, 01:05 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
At the switch:
  • White to White
  • Black of power in pigtailed to one screw of each switche.
  • Black of 3-conductor cable to remaining screw of one switch.
  • Red to remaining screw of the other switch.
At the receptacle:
  • White to silver screw. (Tab is not removed.)
  • Remove tab brass side only.
  • Red to one brass screw.
  • Black to other brass screws.
Grounds connected per code.
 
  #5  
Old 04-28-15, 07:12 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,976
Received 194 Upvotes on 170 Posts
The receptacles need to be weather resistant rated and a in use cover used.
 
  #6  
Old 04-28-15, 08:17 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,928
Received 3,947 Upvotes on 3,540 Posts
A diagram to go along with Ray's description.
Grounds are not shown but are expected to be connected.

Name:  circuit2.jpg
Views: 607
Size:  18.3 KB

You'll need to break the bridge clip off on the hot (gold screw) side of the receptacle.

Name:  bridging clip.jpg
Views: 314
Size:  20.3 KB
 
 