Kitchen Remodel Wiring
Here is the plan:
1. 48" stove dedicated on 50amp/240v
2. 48" fridge (10amps) and 3 outlets (pantry room) on 15amp
3. 48" hood (9amps) and 8 inside cabinets lights (puck) on 15amp
4. dishwasher (1300w, 12amps) dedicated on 15amp
5. main sink disposal (7amps) dedicated on 15amp
6. under cabinet microwave on island (1000w,14.5aamps) dedicated on 20amp
7. island sink disposal (7amps) and 4-5 GFCI (on island) outlets on 15amp
8. under cabinet lights (13 ft of rope light @12.2w/3.3ft) and recessed lights (12 led - 12w each) on 20amp
9. 7 GFCI outlets on a dedicated 20amp
Questions:
Do I need to split Anything?
Can I Combine 4 and 5 and switch to 20amp breaker?
Can I combine 6 and 7?
Is 20amp enough for #8?
Thank you!!!!
1. 48" stove dedicated on 50amp/240v
2. 48" fridge (10amps) and 3 outlets (pantry room) on 15amp
3. 48" hood (9amps) and 8 inside cabinets lights (puck) on 15amp
4. dishwasher (1300w, 12amps) dedicated on 15amp
5. main sink disposal (7amps) dedicated on 15amp
6. under cabinet microwave on island (1000w,14.5aamps) dedicated on 20amp
7. island sink disposal (7amps) and 4-5 GFCI (on island) outlets on 15amp
8. under cabinet lights (13 ft of rope light @12.2w/3.3ft) and recessed lights (12 led - 12w each) on 20amp
9. 7 GFCI outlets on a dedicated 20amp
Questions:
Do I need to split Anything?
Can I Combine 4 and 5 and switch to 20amp breaker?
Can I combine 6 and 7?
Is 20amp enough for #8?
Thank you!!!!
#2
Both small appliance receptacle circuits(you must have 2) must be GFCI protected and of 20 amps in size. I would not put that refrigerator on a 15 amp circuit. Motor start up may cause it to trip. Make it a 20 amp dedicated circuit, as well as the pantry receptacles on a 15 amp. Your island receptacle(s) will need to be part of the GFCI protected 20 amp small appliance circuits, or on a dedicated one by itself.
#8 can be reduced to 15 amp and 14 gauge wiring.
#8 can be reduced to 15 amp and 14 gauge wiring.
#4
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
While the NEC requires two Small Appliance Branch Circuits (SABCs) I think that is woefully inadequate and I would use either three or four such circuits.
Receptacles in pantries are specifically stated as being part of the required SABCs, as such they need to be wired with #12 and on a 20 ampere circuit.
I don't know for certain but I don't think that hard-wired appliances (dishwasher, garbage grinder, need to have GFCI protection. On the other hand, it certainly won't hurt to include it.
Receptacles in pantries are specifically stated as being part of the required SABCs, as such they need to be wired with #12 and on a 20 ampere circuit.
I don't know for certain but I don't think that hard-wired appliances (dishwasher, garbage grinder, need to have GFCI protection. On the other hand, it certainly won't hurt to include it.
#5
Member
Thread Starter
Join Date: Mar 2015
Posts: 30
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Update:
1 48" stove dedicated on 50amp/240v
2 48" fridge (10amps) and 1 outlets (pantry room) and 1 GFCI in Kitchen on 20amp
3 48" hood (9amps) and 8 inside cabinets lights (puck 4.4w each, 35.2w total) on 20amp
4 dishwasher (1300w, 12amps) dedicated on 15amp
5 main sink disposal (7amps) dedicated on 15amp
6 under cabinet microwave on island (1000w,14.5aamps) dedicated on 15amp
7 island sink disposal (7amps) and 4-5 GFCI (on island) outlets on 20amp
8 undercabinet lights (13 feet of rope light @12.2w/3.3ft = 48.06w) and recessed lights (12 led - 12w each = 144w) on 20amp == 192.1 TOTAL WATT)
9 7 GFCI outlets on a dedicated 20amp
1 48" stove dedicated on 50amp/240v
2 48" fridge (10amps) and 1 outlets (pantry room) and 1 GFCI in Kitchen on 20amp
3 48" hood (9amps) and 8 inside cabinets lights (puck 4.4w each, 35.2w total) on 20amp
4 dishwasher (1300w, 12amps) dedicated on 15amp
5 main sink disposal (7amps) dedicated on 15amp
6 under cabinet microwave on island (1000w,14.5aamps) dedicated on 15amp
7 island sink disposal (7amps) and 4-5 GFCI (on island) outlets on 20amp
8 undercabinet lights (13 feet of rope light @12.2w/3.3ft = 48.06w) and recessed lights (12 led - 12w each = 144w) on 20amp == 192.1 TOTAL WATT)
9 7 GFCI outlets on a dedicated 20amp
#6
Depending on the pantry's location. Adjacent to the countertops, I'd concur, but I was picturing a separate room dislocated from the kitchen (old school). Also it will depend on your panel as to whether you can use tandem breakers, freeing up a slot with a slot, so to speak. Tell us the brand and model of your panel or look on the door to see if it will accept tandem breakers and where they can be located on the busses.
#9
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
Depending on the pantry's location.
BTW, the pantry is a separate room next to the kitchen with a separate entrance separated by a 4.5" wall.
The reasoning is that in all these locations there could be a refrigerator, a coffee pot, a toaster, a roaster or other such cooking appliance.
#13
Member
Thread Starter
Join Date: Mar 2015
Posts: 30
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Dishwasher wiring
Can i Put a DW (1300w,12amp) on a circuit that was used before as a stove hood vent (the one that comes out of a counter top). it also has a 120v outlet attached for the gas range. The circuit is using 2 connected breakers (total 30amp).
Can i modify it somehow to use for my DW?
Thanks in advance.
Can i modify it somehow to use for my DW?
Thanks in advance.
#14
This is a little advanced wiring.
Can you explain what wires you have at the box where power comes from the panel.
Do you have:
1 black
1 red
1 white
Bare Ground?
If so, you can run 2 each 120V circuits from this box and change the breaker to a double pole.
Post a picture if you can.
Can you explain what wires you have at the box where power comes from the panel.
Do you have:
1 black
1 red
1 white
Bare Ground?
If so, you can run 2 each 120V circuits from this box and change the breaker to a double pole.
Post a picture if you can.
Last edited by pcboss; 04-30-15 at 11:22 AM.
#15
The circuit is using 2 connected breakers (total 30amp).
#16
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
It doesn't need to be a separate circuit, but it does need to be part of one of the two required small appliance branch circuits. It could be part of the circuit supplying power to the island or the counter top receptacles.
#17
At least two circuits for the island. One receptacle and one for the GD. The microwave can be powered by one of the 20 amp small appliance circuits, unless the instructions call for a dedicated circuit.
This is one area the code is too lenient IMO.
This is one area the code is too lenient IMO.
#21
Member
Thread Starter
Join Date: Mar 2015
Posts: 30
Upvotes: 0
Received 0 Upvotes
on
0 Posts
my fault.. not DW.
On The Island:
I have a MW, GD and 3 GFCI outlets.. I have 2 dedicated circuits available(15amp and 20amp).. can i use them or do i need another 15amp for a total of 3?
an addition question, not on the island... I have a 9amp range hood, what can i connect that to? do i need separate circuit? i have a 20 amp circuit avail that has 3 GFCI on it.. can i use it?
On The Island:
I have a MW, GD and 3 GFCI outlets.. I have 2 dedicated circuits available(15amp and 20amp).. can i use them or do i need another 15amp for a total of 3?
an addition question, not on the island... I have a 9amp range hood, what can i connect that to? do i need separate circuit? i have a 20 amp circuit avail that has 3 GFCI on it.. can i use it?
#22
I have a MW, GD and 3 GFCI outlets.. I have 2 dedicated circuits available(15amp and 20amp).. can i use them or do i need another 15amp for a total of 3
I have a 9amp range hood, what can i connect that to
#23
Member
Thread Starter
Join Date: Mar 2015
Posts: 30
Upvotes: 0
Received 0 Upvotes
on
0 Posts
MW = microwave (14.5amp)
GD = (7amps)
So i need a third circuit on island either dedicated or SABC for the 3 GFCI.
And for the hood...9amps cant go on 20amp because its more than 80% of 20?
regarding my DW:
Can i somehow modify a dedicated circuit (30amp from gas range pullout vent) for my dishwasher (12amp)? there is a 120v outlet attached to the 30amp for the gas range.. or do i need to run another line?
GD = (7amps)
So i need a third circuit on island either dedicated or SABC for the 3 GFCI.
And for the hood...9amps cant go on 20amp because its more than 80% of 20?
regarding my DW:
Can i somehow modify a dedicated circuit (30amp from gas range pullout vent) for my dishwasher (12amp)? there is a 120v outlet attached to the 30amp for the gas range.. or do i need to run another line?
#24
Member
Thread Starter
Join Date: Mar 2015
Posts: 30
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Ok, the handles are tied together (already double pole??), with 30 amps written twice on handle.
Red wire coming into one part of it, black into the other part of it. there is a white and bare as well i'm assuming.
There is a 120v outlet attached under the gas stove...i'm thinking 120v for the pilot lights and 120v for the vent.
How can I convert this my 120v dishwasher somehow?
Red wire coming into one part of it, black into the other part of it. there is a white and bare as well i'm assuming.
There is a 120v outlet attached under the gas stove...i'm thinking 120v for the pilot lights and 120v for the vent.
How can I convert this my 120v dishwasher somehow?
#25
You will need to change the breaker to a 2 pole 15 or 20.
You will need to find where the cable runs. Once you can tell us that more information can be given. Basically you will run from where the cable splits into the two circuits to the DW and install a receptacle in the cabinet next to the DW.
You will need to find where the cable runs. Once you can tell us that more information can be given. Basically you will run from where the cable splits into the two circuits to the DW and install a receptacle in the cabinet next to the DW.
#26
The hood cannot go on the 20 amp small appliance circuit due to code rules that those serve only receptacle loads. The hood is fixed in place.
Island circuits: 1 MW, 1 20 amp for receptacles with gfi protection, 1 for GD.
I have never seen a gas range that needed 30 amps. Normally they only need power for the clock and the ignitor.
Island circuits: 1 MW, 1 20 amp for receptacles with gfi protection, 1 for GD.
I have never seen a gas range that needed 30 amps. Normally they only need power for the clock and the ignitor.
#27
Member
Thread Starter
Join Date: Mar 2015
Posts: 30
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I have a gas range with a vent behind it that pops up when you press a button.
The range I can see plugs into a 120V under the cabinet. I'm assuming the vent is 120v, but its a direct connection.
I just need 120V for the DW, what can I do?
The range I can see plugs into a 120V under the cabinet. I'm assuming the vent is 120v, but its a direct connection.
I just need 120V for the DW, what can I do?
#29
Member
Thread Starter
Join Date: Mar 2015
Posts: 30
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I have a gas range with a vent behind it that pops up when you press a button.
The range I can see plugs into a 120V under the cabinet. I'm assuming the vent is 120v, but its a direct connection.
I just need 120V for the DW, what can I do?
From Previous Post:
I don't get it.. please explain...the hood plugs into a receptacle?
The range I can see plugs into a 120V under the cabinet. I'm assuming the vent is 120v, but its a direct connection.
I just need 120V for the DW, what can I do?
From Previous Post:
I don't get it.. please explain...the hood plugs into a receptacle?
#33
I don't get it.. please explain...the hood plugs into a receptacle?
my GD is 15amp
You need to bite the bullet here. You have lots of high amp appliances that are going to need their own circuits. No way around it.
#34
Member
Thread Starter
Join Date: Mar 2015
Posts: 30
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Understood about hood. will put in its own.
about the GB, its on a 15amp circuit.. so I cant add the DW on it.
I need to use the 30amp double pole, and split it so I can hook it up to the DW and hood.
I would like to use the same wire from stove vent, the DW will be in the stove's place.. but I only need 15amp, 120V for the DW.
I can actually use the other 15amp, 120V for the hood, but i need to extend it. finished basement ;(
how do i split the panel and the wire on the other end?
about the GB, its on a 15amp circuit.. so I cant add the DW on it.
I need to use the 30amp double pole, and split it so I can hook it up to the DW and hood.
I would like to use the same wire from stove vent, the DW will be in the stove's place.. but I only need 15amp, 120V for the DW.
I can actually use the other 15amp, 120V for the hood, but i need to extend it. finished basement ;(
how do i split the panel and the wire on the other end?
#36
I need to use the 30amp double pole, and split it so I can hook it up to the DW.
The 30 amp breaker is almost certainly a fire hazard that needs to be removed and should never have been used.
Information: There are few residential devices that are120v/30a. If they do need a 30 amp feed they are used on 30 amp circuits fed by #10 minimum and require special receptacles and plugs. These plugs and receptacles are different from and not comparable with 120 volt 15a and 20a receptacles and plugs. Devices intended for general purpose 15a and 20a 120 volt circuits should never be used on 30 amp circuits. You have nothing that should be on a 30 amp circuit.
Last edited by ray2047; 04-30-15 at 03:07 PM.
#37
This is confusing because of all the code requirements discussed. I think you understand that and forget it for now.
It sounds to me like you previously had a gas cook top with telescoping (electric) downdraft vent, and want to change it to a freestanding gas range.
Many homes were set up to accommodate both gas and electric cook tops, or ranges, ovens, whatever.
IF you have a junction box in the area of old cook top, containing 10/3 with ground (most likely), wired to a double pole 30amp breaker, post back for instructions on how to convert this into 2 each 120V circuits.
Very simple and having wiring like this nearby has saved me many times.
See post 25.
It sounds to me like you previously had a gas cook top with telescoping (electric) downdraft vent, and want to change it to a freestanding gas range.
Many homes were set up to accommodate both gas and electric cook tops, or ranges, ovens, whatever.
IF you have a junction box in the area of old cook top, containing 10/3 with ground (most likely), wired to a double pole 30amp breaker, post back for instructions on how to convert this into 2 each 120V circuits.
Very simple and having wiring like this nearby has saved me many times.
See post 25.
#38
Member
Thread Starter
Join Date: Mar 2015
Posts: 30
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I will try to post some pics. The house was build (1989) with the gas cook top and downdraft vent.. exactly.
Now i want to change to freestanding range, but its 10 feet away and its all wired, I'm good with that.
Where the old gas cooktop was, now will be a DW and I dont have a dedicated 120v line there. I can either run a new one (about 80ft through finished basement, or use the old cook top connection).
I checked under the cook top and i don't see where line comes in from the floor (I will be removing that part soon).... but I do see a line from the bottom of the vent to a 120v receptacle. and the wire looks thin, probably 12 or even 14. There is power cord for the gas cooktop that plugs into this 120v for lighting the burners.
BTW... On the downdraft vent sticker.. its says 120v!
The only way this receptacle turns OFF on the main panel is when i turn OFF the 30amp double connected breaker. i dont see anything else connected to the 30amp anywhere in the house.
can i break the 30amp into 2 15amp or 20amp.. will that depend on the wire size?
go figure...
Now i want to change to freestanding range, but its 10 feet away and its all wired, I'm good with that.
Where the old gas cooktop was, now will be a DW and I dont have a dedicated 120v line there. I can either run a new one (about 80ft through finished basement, or use the old cook top connection).
I checked under the cook top and i don't see where line comes in from the floor (I will be removing that part soon).... but I do see a line from the bottom of the vent to a 120v receptacle. and the wire looks thin, probably 12 or even 14. There is power cord for the gas cooktop that plugs into this 120v for lighting the burners.
BTW... On the downdraft vent sticker.. its says 120v!
The only way this receptacle turns OFF on the main panel is when i turn OFF the 30amp double connected breaker. i dont see anything else connected to the 30amp anywhere in the house.
can i break the 30amp into 2 15amp or 20amp.. will that depend on the wire size?
go figure...
#39
can i break the 30amp into 2 15amp or 20amp.
IF you have a junction box in the area of old cook top, containing 10/3 with ground (most likely), wired to a double pole 30amp breaker, post back for instructions on how to convert this into 2 each 120V circuits.
#40
This is confusing because of all the code requirements discussed.