Wiring in the Garage

I installed a gable fan in the attic last year. I used Romex (12 gauge).

I will be installing a gable fan in the garage this year and I understand that Romex CANNOT be used in the garage unless it is behind drywall.

I will be installing an electrical box on top of the drywall, over an existing box (single receptacle), which I will expand to two receptacles.
Steel City 2-Gang Square Electrical Box-521711234EW-25R - The Home Depot

From there, I think the option will either be conduit or armor cable, connected to this electrical box. Please provide your thoughts or recommendation? I am thinking of using armor cable but is there anything more I need to know? I google "armor cable" and AC and MC came up. Any pointers here would be appreciate it. Conduit in the garage just seems like an overkill.

Thanks
 
Sponsored Links
  #2  
Old 04-30-15, 09:33 AM
WRDIY's Avatar
Member
Thread Starter
Join Date: Jul 2012
Posts: 620
Actually, can I wire the gable fan to a dedicated extension cord (in a junction box) and plug it into the outlet?
 
  #3  
Old 04-30-15, 09:44 AM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,044
can I wire the gable fan to a dedicated extension cord (in a junction box) and plug it into the outlet?
No. Extension cords are for temporary use only.
I will be installing a gable fan in the garage this year and I understand that Romex CANNOT be used in the garage unless it is behind drywall.
It can be if protected. You could put an extension ring on a receptacle and use PVC conduit to protect it to a height where protection isn't required.. Above 6'7" NM-b can usually be run without protection.
 
  #4  
Old 04-30-15, 09:56 AM
WRDIY's Avatar
Member
Thread Starter
Join Date: Jul 2012
Posts: 620
Thank you Ray! I just learned something new:

It can be if protected. You could put an extension ring on a receptacle and use PVC conduit to protect it to a height where protection isn't required.. Above 6'7" NM-b can usually be run without protection.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes