I am interested to know how large of an inverter (DC to AC) would be recommended for a 10 AMP ac initial surge and 6 AMP run. The 6 AMP run would be for about two to three minutes, once maybe twice a day at different intervals. Would a 1K watt suffice or should I go larger? I am planning to use a heavy duty battery pack or 12vdc battery to run the inverter. My application is running a vacumn cleaner motor that pumps air into a tank to raise a boat lift. I measured amps with a UEI meter. Thanks
 
  #2  
Old 05-10-15, 10:10 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,758
Received 676 Upvotes on 573 Posts
At 10 amps your surge is 1200 watts. The surge or peak of the inverter should be at least that. I would recommend going a little higher (1500-2000w peak) as it seams that some manufactures overstate their products specs.

Is this a shop vac motor? 6 amps seams a little light if it is.
 
  #3  
Old 05-10-15, 10:13 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,102
Received 3,424 Upvotes on 3,070 Posts
I agree with Tolyn..... go with at least a 1500 watt inverter.
 
  #4  
Old 05-10-15, 10:16 AM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 36,608
Upvotes: 0
Received 9 Upvotes on 8 Posts
The only thing I question is the application. I just don't think a vacuum cleaner motor will have enough power to lift a boat.
 
  #5  
Old 05-10-15, 10:50 AM
S
Member
Thread Starter
Join Date: Jul 2014
Posts: 36
Upvotes: 0
Received 0 Upvotes on 0 Posts
OK, I will go a little higher, will shop for a 1500 and preferably 2000. Yes, common application with many lifts is a fairly large tank and a vacuum cleaner motor that simply pumps air. Thanks folks, appreciate the replies
 
  #6  
Old 05-10-15, 11:01 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,102
Received 3,424 Upvotes on 3,070 Posts
That's extremely interesting. Vacuum cleaner motors are known for their sucking power.... they are not known for their blowing power.
 
  #7  
Old 05-10-15, 11:13 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,758
Received 676 Upvotes on 573 Posts
I recall wiring a truck dock leveler that was air powered rather then spring or hydraulic. Sounded just like a vacuum and worked quite well.
 
  #8  
Old 05-10-15, 03:13 PM
M
Member
Join Date: Sep 2009
Location: Louisville KY
Posts: 514
Received 1 Upvote on 1 Post
I recall wiring a truck dock leveler that was air powered rather then spring or hydraulic. Sounded just like a vacuum and worked quite well.
The plant that I retired from had just about converted everything to those kind of levelers. They seem to have fewer problems than the other types, are easier to work on when they have a problem and are less expensive to purchase. They basically use an airbag like rescue services used to lift cars at accident scenes, the year is provided by a system that is much like that in a shop vac. They actually keep a spare bag and motor around and can swap them out in less than 30 minutes if they have a problem.
 
 