inverter wiring

The Morningstar 300 Inverter and many others have an internal bond of its neutral out/white
and ground. If you look at the unit documentation online you can see that.
If you want to run this inverters output to a service panel,offgrid, you want to make sure to disconnect the neutral/ground bond in the panel because you only want one bond.
But what if you run the ground on the Morningstar to a separate ground rod not connected to the panel ground rod. I happen to have 2 different rods about 40 ft apart.
are you ok then just leaving the panel bond tied as normal..???
 
  #2  
Old 05-10-15, 08:03 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
You seem to be confusing GEC and EGC. Ground wires in the house are for EGC. Ground rods are for the GEC
 
  #3  
Old 05-11-15, 01:50 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,046
Received 159 Upvotes on 145 Posts
What are you trying to achieve?
Geo
 
 