inverter wiring

Reply

  #1  
Old 05-10-15, 07:45 PM
Member
Thread Starter
Join Date: Feb 2015
Posts: 197
inverter wiring

The Morningstar 300 Inverter and many others have an internal bond of its neutral out/white
and ground. If you look at the unit documentation online you can see that.
If you want to run this inverters output to a service panel,offgrid, you want to make sure to disconnect the neutral/ground bond in the panel because you only want one bond.
But what if you run the ground on the Morningstar to a separate ground rod not connected to the panel ground rod. I happen to have 2 different rods about 40 ft apart.
are you ok then just leaving the panel bond tied as normal..???
 
Sponsored Links
  #2  
Old 05-10-15, 08:03 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,050
You seem to be confusing GEC and EGC. Ground wires in the house are for EGC. Ground rods are for the GEC
 
  #3  
Old 05-11-15, 01:50 PM
Member
Join Date: Nov 2012
Location: USA
Posts: 3,314
What are you trying to achieve?
Geo
 