Feed Shed from Spa Panel

I'm adding a spa which I plan to feed from a 60A GFCI in the main panel which will feed a spa disconnect with 6/3 NMD. From that point a 50 amp breaker will feed the hot tub with #6 THHN and #8 Grnd. The spa panel has extra spaces and I'd like to feed my shed which is 30 feet away with a 15A breaker.

The shed has 4 lights and 2 outlets. Does anyone think the inspector will have an issue with this?

EDIT: This is in Canada so CEC applies.
 
  #2  
Old 05-11-15, 06:30 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
The panel load should be based on total calculated load. If the load of the spa plus the expected load in the garage is less than 60A, it should be ok.
 
  #3  
Old 05-11-15, 05:49 PM
D
Member
Thread Starter
Join Date: Jul 2013
Location: Canada
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
I'm waiting to hear back from the manufacturer regarding the actual draw of the tub. The shed has 4 led pot lights and one incandescent inside so I don't see load being an issue. I will do a load Calculation once I hear back.

Thanks.
 
  #4  
Old 05-11-15, 06:28 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,923
Received 177 Upvotes on 155 Posts
You might want to check to see if a bare ground is allowed. In the US there are restrictions on the bare ground and spas.
 
 