While updating some electrical in my home, it was discovered that some of the outlets were 12/2 wiring with 15 amp outlets. I decided to install the proper 20 amp outlets to those receptacles.
Of course I turned off the breaker to the outlet, then tested with one of those plug in testers..no lights. However, once I removed the plate and pulled out the outlet, I tested again with a voltage tester. There are 2 black wires, 2 white wires and the grounds. The white wires were still hot. I found the other circuit and turned it off. I'm just questioning why and/or if this is ok to wire back as is.
For the record, it is apparent someone previously, in an effort to appear updated, went around and replaced a majority of the switches and outlets and even added green ground wires in some receptacles. Obviously not aware of wire gauge or the function of the wiring.
Of course I turned off the breaker to the outlet, then tested with one of those plug in testers..no lights. However, once I removed the plate and pulled out the outlet, I tested again with a voltage tester. There are 2 black wires, 2 white wires and the grounds. The white wires were still hot. I found the other circuit and turned it off. I'm just questioning why and/or if this is ok to wire back as is.
For the record, it is apparent someone previously, in an effort to appear updated, went around and replaced a majority of the switches and outlets and even added green ground wires in some receptacles. Obviously not aware of wire gauge or the function of the wiring.
#2
it was discovered that some of the outlets were 12/2 wiring with 15 amp outlets. I decided to install the proper 20 amp outlets to those receptacles.
it is apparent someone previously, in an effort to appear updated, went around and replaced a majority of the switches and outlets and even added green ground wires in some receptacles.
Note when two circuits terminate in the same box neutrals must be kept separate but all ground regardless of circuit must be connected together.
#3
Good to know on the 15 amp receptacles and cable types.
As for the two circuit outlet, it's ok to wire it back as it was then? Each white wire on its own terminal, same for the black, and the grounds together? The connection tab on the outlet does not need to be broken?
As for the two circuit outlet, it's ok to wire it back as it was then? Each white wire on its own terminal, same for the black, and the grounds together? The connection tab on the outlet does not need to be broken?
#4
The connection tab on the outlet does not need to be broken?
when two circuits terminate in the same box neutrals must be kept separate
#5
I think you may arrived in the middle of a multiwire branch circuit where two circuits share the same neutrals. Once you opened the neutral the second live circuit lost its neutral and the neutral wire would become hot due to a connected load.
The way to determine if this is a MWBC is to look at the panel.... if the two breakers are one over the other then it's very likely. You could further verify by opening the panel cover to see if one breaker has a red wire on it and the other has a black wire on it.
It is possible that two circuits were connected to that receptacle and if that is the case the bridge clips would be broken off the sides.

The reason I don't think this is your case since you said the circuits in the box were dead when you turned off the first breaker.
The way to determine if this is a MWBC is to look at the panel.... if the two breakers are one over the other then it's very likely. You could further verify by opening the panel cover to see if one breaker has a red wire on it and the other has a black wire on it.
It is possible that two circuits were connected to that receptacle and if that is the case the bridge clips would be broken off the sides.

The reason I don't think this is your case since you said the circuits in the box were dead when you turned off the first breaker.
#6
PJmax, the two breakers are not above one another and there are no red wires. Actually, the first circuit that powers the outlet is a 20 amp. The 2nd circuit is 15 amp. All the wires in this outlet are 12 gauge. I don't understand how this 2nd circuit fits in. More importantly, is it safe to wire it back the way it was?
#7
What kind of tester was used to determine the wires were hot after you turned off the first breaker?
#8
PJmax, the two breakers are not above one another and there are no red wires
When you say there are no red wires, do you mean inside the main panel? It doesn't matter that there are no red wires in the receptacle box, you need to check the breaker wires.
Also, MWBC breakers might not be adjacent, especially in an older home. If installed properly the breakers will be on opposite legs in panel, but not necessarily adjacent.
#9
pcboss, one of those pen type voltage testers that light up and beep when in contact with a hot wire.
#10
Handyone, There are no red wires in the panel at all. The breakers are on opposite sides (23 & 8). I had the panel upgraded last spring by a licensed electrician. They did add some new wiring, primarily in the basement that is being renovated, but any other wiring that existed in the panel was simply wired back in.
I do know that one of the cables going into this outlet runs into a junction box that joins 2 other outlets and feed from the panel (circuit 23). The other cable goes to an outlet about 4 feet away but it's on the exterior of the house. Also, the other circuit (8) happens to feed the lights and outlets on the opposite side of the same room as the outlet in question.
I do know that one of the cables going into this outlet runs into a junction box that joins 2 other outlets and feed from the panel (circuit 23). The other cable goes to an outlet about 4 feet away but it's on the exterior of the house. Also, the other circuit (8) happens to feed the lights and outlets on the opposite side of the same room as the outlet in question.
#11
pcboss, one of those pen type voltage testers that light up and beep when in contact with a hot wire.
#12
The breakers are on opposite sides (23 & 8).
This is basic stuff, your electrician should have known this.