Electrical panel ground/neutral bus bar question
#1
Member
Thread Starter
Join Date: May 2015
Location: USA
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Electrical panel ground/neutral bus bar question
In CH type panel CMBE4242B200BTS ( main bus is Copper) , I am trying to replace AL ground/neutral bus bar with copper bus.
The current Ground/Neutral bus in the panel is Tin plated Aluminum ( 6061-T6).
All my wiring is copper. Do you guys see any issues with this ?
Thanks
Diwakar
The current Ground/Neutral bus in the panel is Tin plated Aluminum ( 6061-T6).
All my wiring is copper. Do you guys see any issues with this ?
Thanks
Diwakar
#2
Welcome to the forums.
Absolutely none. The panel was designed to be used with that type bar and copper wiring.
I've seen diecast bars but not copper ones in many years.
Are you sure the bars are aluminum..... I couldn't find any description or specs on them ?
Do you guys see any issues with this ?
I've seen diecast bars but not copper ones in many years.
Are you sure the bars are aluminum..... I couldn't find any description or specs on them ?
#3
Member
Thread Starter
Join Date: May 2015
Location: USA
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks.
The part is ILSCO ( 8108-86), catalog (NBAE 0924-2).
http://www.ilsco.com/documents/PDF/T...wing/N8108.pdf
which is tin plated aluminum (6061-T6) for ground/neutral bar
I am planning to replace it with "ILSCO N174" which is copper only bar.
My concern is it's connection to panel and to clamp.
The part is ILSCO ( 8108-86), catalog (NBAE 0924-2).
http://www.ilsco.com/documents/PDF/T...wing/N8108.pdf
which is tin plated aluminum (6061-T6) for ground/neutral bar
I am planning to replace it with "ILSCO N174" which is copper only bar.
My concern is it's connection to panel and to clamp.
#5
Do you guys see any issues with this ?
That's a nice looking piece of equipment. Sliver plated copper bus to accept the breakers is the best way to go in my opinion.
#6
Member
Thread Starter
Join Date: May 2015
Location: USA
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks for comments guys.
I am specifically looking to do it from audio perspective. It may not make any difference but I am trying to reduce the resistance in ground path ( Ground/neutral bar shorted)
This will be my main panel.
I am specifically looking to do it from audio perspective. It may not make any difference but I am trying to reduce the resistance in ground path ( Ground/neutral bar shorted)
This will be my main panel.
#8
Member
Thread Starter
Join Date: May 2015
Location: USA
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I agree on that front. I will probably leave it as is.
Naive question though, from that perspective, how people buy/replace/use "off the shelf( from leading manufactures) " copper ground/bars since no panel these days are equipped it anyways ?
Naive question though, from that perspective, how people buy/replace/use "off the shelf( from leading manufactures) " copper ground/bars since no panel these days are equipped it anyways ?
#9
Naive question though, from that perspective, how people buy/replace/use "off the shelf( from leading manufactures) " copper ground/bars since no panel these days are equipped it anyways ?
It may not make any difference but I am trying to reduce the resistance in ground path ( Ground/neutral bar shorted)
#10
Member
Thread Starter
Join Date: May 2015
Location: USA
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I doubt it myself too, but it doesn't cost much to replace those bars anyways as long as it doesn't violate the UL listing of the panel.
By the way, 6061-T6 has about 45% conductivity of copper.
By the way, 6061-T6 has about 45% conductivity of copper.
#11
When aluminum conductors are used they are larger than copper for the same ampacity to make up for the difference.
#12
Member
Thread Starter
Join Date: May 2015
Location: USA
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
My question
Hi,
Can I replace neutral/Ground (Tin plated aluminum) in
CMBE4242B200BTS panel with ILSCO copper bars ?
Thanks
Reply from Eaton
Since it’s a service entrance panel, the neutral/ground is bonded, so I don’t see any issue with changing to a different ground bar. However if any inspector noticed the difference and called you out on it, we don’t have anything official documentation to back you up in doing this. So I would suggest you hold onto the original neutral/ground in case the inspector says you can’t change it.
Hi,
Can I replace neutral/Ground (Tin plated aluminum) in
CMBE4242B200BTS panel with ILSCO copper bars ?
Thanks
Reply from Eaton
Since it’s a service entrance panel, the neutral/ground is bonded, so I don’t see any issue with changing to a different ground bar. However if any inspector noticed the difference and called you out on it, we don’t have anything official documentation to back you up in doing this. So I would suggest you hold onto the original neutral/ground in case the inspector says you can’t change it.