Dead GFI receptacle- other outlets on circuit fine

A bathroom receptacle suddenly stopped working. It was a GFCI, and resetting it did nothing. No other outlets seem to be affected, no breaker was thrown. I removed the GFCI and measured the voltages (Fluke 175).
With the breaker on:
Hot-GND: 5.6 V
Hot-Neu : 0.9 V
Neu-GND: 4.7 V
With the breaker off:
Hot-GND: 3.9 V
Hot-Neu : 0.6 V
Neu-GND: 3.3 V

Any ideas on what could be wrong/how to fix this?
 

Last edited by deserthome; 05-16-15 at 06:51 PM. Reason: error
Sponsored Links
  #2  
Old 05-16-15, 09:27 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: NJ - USA
Posts: 43,439
Welcome to the forums.

Basically with those measurements you are lacking your 120vac hot line.
Did you have your meter set to AC voltage..... not DC voltage ?

Name:  obr1371_4.jpg
Views: 67
Size:  21.5 KB

You will need to determine what else is on that circuit. If the problem is not there then it is at the last working device before that one.
 