so many people have different ideas of proper grounds ..... Here is another scenario.
If you install a small solar system (not tied to your grid system at all)at your house for power back up and you want to ground the inverter and panels/batteries
on the back roof and the grid service ground is 100 ft away....you put in another ground rod out back.
But some people say that in the event of lightning you can create an imbalance problem between
the 2 ground rods if they are not connected by a wire.Voltage can build up between them due to potential difference and damage equipment. Even if the 2 systems are totally different and not connected at all.
Is it really that bad to do this,install another rod, if you install a lightning arrest unit as part of the solar system??
 
Sponsored Links
  #2  
Old 05-25-15, 07:58 PM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,356
Yes, in the event of a near by lightning strike you can have a voltage difference between the two grounding electrodes. Yes, installations without a bond are done all the time, sometimes with no harm and other times with disastrous results.

In case of a direct strike you should hope to have a goose in between the two systems because it will be cooked.
 
  #3  
Old 05-26-15, 02:30 PM
Member
Join Date: Mar 2010
Location: USA
Posts: 2,849
A solar power system or generator system with all separate wiring and receptacles and with no proximity of conductors or components let alone transfer switch or other interconnection with any other wiring involving ground rods would not need its ground rod to be bonded to such other ground rods.

Code requires that if you have more than one ground rod being used for anything or something or other including antennas connected to radios powered by the home electrical system then all rods most be interconnected using #6 copper wire or equivalent.

Exception: Any such grounding electrode conductors that would have to cross lawns, sidewalks, etc. to get to rods for different buildings may be summarily omitted.

The grounding electrode conductors described here give an easier path for voltage differentials across horizontal distance on the ground that are likely to exist momentarily in the vicinity of lightning strikes to dissipate without using and burning up coax shields or equipment grounding conductors or (by jumping through insulation) using juxtaposed current carrying conductors of wiring inside the house.
 

Last edited by AllanJ; 05-26-15 at 02:59 PM.
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
'