Adding More AC Smoke Detectors
Old 05-25-15, 08:07 PM
G
Gen
Gen is offline
Received 16 Upvotes on 11 Posts
Hello, I have to add 2 more smoke detectors to satisfy the ones needed inside bedrooms. Question is: can I jumper a 14-3 wire (if enough room in box) from one existing smoke to a new location, then jump from there to another new location? It is on the upper floor so I am able to work from the attic to do this. Also I plan to start with all new smokes for compatibility. Thanks very much!
Old 05-25-15, 08:16 PM
F
Assuming the originating smoke detector is on a 15 ampere circuit, then yes, you can use 14-3 cable to interconnect all three detectors. Be sure to follow the wiring diagram included with the new detectors.
Old 05-25-15, 08:21 PM
G
Gen
Gen is offline
OK thank....yes 15A......will this work ok even if there are 3 other existing locations? I'm staring the jumpering from one of them, and assume it does not matter which one.
Old 05-25-15, 08:45 PM
F
All smoke detectors need to wired together with three-conductor cable if they are to communicate with each other. If the original detectors are only connected with a two-conductor cable (no red wire) then they will not alert the new detectors in case of fire at the now existing locations. Neither will the older detectors alert if there is a fire at the new detector locations.
Does that answer your question?
Old 05-25-15, 08:58 PM
Received 3,973 Upvotes on 3,566 Posts
That is an excellent idea.
Old 05-26-15, 01:56 AM
pcboss's Avatar
Received 194 Upvotes on 170 Posts
As long as the maximum number of devices is not exceeded your plan is good.
Old 05-26-15, 04:36 AM
G
Gen
Gen is offline
Yes..all questions have been answered. (It is existing 14-3 and interconnected) Essentially I wanted to know if it was OK to jumper from any existing location, and that seems to be the case. Thanks very much.