3-way switch--poles switch?
Hello,
I've been struggling with a 3-way switch dilemma for nearly a week and can't seem to find an answer online.
I have 2 3-way switches hooked up to a receptacle. Both switches work fine, and that receptacle gets power just fine. The problem starts when I put a tester on it and find that the neutral becomes hot when I turn switch 'A' on (copper side becomes cold) and reverses when I turn switch 'B' on.
Does a 3-way switch basically switch from pole to pole, positive to negative?
Thanks.
I've been struggling with a 3-way switch dilemma for nearly a week and can't seem to find an answer online.
I have 2 3-way switches hooked up to a receptacle. Both switches work fine, and that receptacle gets power just fine. The problem starts when I put a tester on it and find that the neutral becomes hot when I turn switch 'A' on (copper side becomes cold) and reverses when I turn switch 'B' on.
Does a 3-way switch basically switch from pole to pole, positive to negative?
Thanks.
#5
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
I rarely respond to any questions concerning three-way switches because they are absurdly simple.
No, because with alternating current there is no positive and negative. Even if you are using a direct current source (battery) the three-way switch does not change from positive to negative.
The ONLY thing a pair of three-way switches do is to offer an alternate path for the electricity to flow upon depending on the positions of the individual switches. Power comes into the common contact of one switch and leaves from the common contact on the other switch. The power will traverse on ONE of the "traveler" wires between the two switches and which traveler is used depends upon the position of the handles of the two switches.
Does a 3-way switch basically switch from pole to pole, positive to negative?
The ONLY thing a pair of three-way switches do is to offer an alternate path for the electricity to flow upon depending on the positions of the individual switches. Power comes into the common contact of one switch and leaves from the common contact on the other switch. The power will traverse on ONE of the "traveler" wires between the two switches and which traveler is used depends upon the position of the handles of the two switches.
#8
Member
Thread Starter
Join Date: May 2015
Posts: 9
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Yet when I hook this up the receptacle will alternate between neutral being hot and the hot being hot.
I know 3 ways are "absurdly simple" which is why I'm here: I've done this so many times there shouldn't be a problem, yet here I have alternating poles.
I'm near losing sleep over this stupid problem. Grrrrr.
I know 3 ways are "absurdly simple" which is why I'm here: I've done this so many times there shouldn't be a problem, yet here I have alternating poles.
I'm near losing sleep over this stupid problem. Grrrrr.
#9
Member
Thread Starter
Join Date: May 2015
Posts: 9
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I'll tell you what's even more strange...the outer metal frame around the switch has zapped me a couple times when the neutral pole registers as being hot.
I'll add that these are 20 amp switches that I have replaced with new ones (in case there was some manufacture error) as well as the receptacle.
I'll add that these are 20 amp switches that I have replaced with new ones (in case there was some manufacture error) as well as the receptacle.
#10
The size of the switch has absolutely nothing to do with this. You said you're getting a shock ?
If the switch is in AND grounded how would you get a shock unless you are missing a ground.
If the switch is in AND grounded how would you get a shock unless you are missing a ground.
#11
Member
Thread Starter
Join Date: May 2015
Posts: 9
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Pjmax
I have no idea. I'm not a spring chicken...everything was grounded.
UPDATE: took all the wiring out of the junction box and hooked it up...now it works fine.
Which makes me mad because I have no idea what the problem was.
Thanks...all!
I have no idea. I'm not a spring chicken...everything was grounded.
UPDATE: took all the wiring out of the junction box and hooked it up...now it works fine.
Which makes me mad because I have no idea what the problem was.
Thanks...all!
#12

It's working but I'm not convinced that you aren't missing the ground to that box.
#14
Member
Thread Starter
Join Date: May 2015
Posts: 9
Upvotes: 0
Received 0 Upvotes
on
0 Posts
UPDATE UPDATE: Found the problem! 
The hot wire from the power had a slit down the side of it and was grounding itself out to the metal junction box. All boxes are metal, all have been grounded properly, but that explains why it switched from neutral to hot and back.
So weird...
I was about to call a priest and a rabbi to bless my garage.

The hot wire from the power had a slit down the side of it and was grounding itself out to the metal junction box. All boxes are metal, all have been grounded properly, but that explains why it switched from neutral to hot and back.
So weird...
I was about to call a priest and a rabbi to bless my garage.
#16
All boxes are metal, all have been grounded properly, but that explains why it switched from neutral to hot and back.