I will admit I have answered this question bur have been corrected also. Doing a search I'm getting conflicting answers. Is it only a service panel? Is it only over 250 volts. Is it concentric or eccentric? Washers?

I'm helping a member in thread http://www.doityourself.com/forum/el...cabinet-2.html.
 
  #2  
Old 06-04-15, 03:17 AM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 36,607
Upvotes: 0
Received 9 Upvotes on 8 Posts
Ray, I may not understand completely, but if the two panels are connected via metal conduit, no grounding bushing is needed, only the plastic chafing bushings where the wires pass through.
 
  #3  
Old 06-04-15, 07:24 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
In a residential situation the only places you'll need to worry about grounding bushings is on the live side of a service entrance when using metal conduit and on both sides of the conduit or protection sleeve the GEC runs through if it is metal. Other than those two fairly rare situations, a metal fitting and lock nut to the electrical box is a sufficient ground. The plastic bushings should be used on any fitting that has sharp edges, such as threaded pipe nipples. Most cast fittings are smooth enough to not need one.
 
  #4  
Old 06-04-15, 08:21 AM
ray2047's Avatar
Member
Thread Starter
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Thank you. .
 
  #5  
Old 06-04-15, 03:11 PM
Mr.Awesome's Avatar
Member
Join Date: Oct 2013
Location: Canada
Posts: 511
Received 0 Upvotes on 0 Posts
Ray,

I think it is just assurance that you have a solid bond on your conduit. Let's say you have a pipe run that ends in a compression coupling and two reducing washers, or a run of liquid tight flex. Can you ensure there is enough connection between your connector and box/panel tub to carry fault current through the pipe run?
Some of the places I've worked at in the middle of nowhere spec'd bonds and ground bushings everywhere just for assurance. Less chance for injured employees 2hrs from the nearest hospital and expensive service calls.
Not saying this is a common problem, but a guess as to why the rules are there.
 
  #6  
Old 06-04-15, 06:36 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,872
Received 185 Upvotes on 166 Posts
Is it only a service panel? Is it only over 250 volts. Is it concentric or eccentric? Washers?
The only place inspectors in my area look for them is on services when metallic conduit is used; heavy wall or EMT. The usual places you'll see them is between meter socket (sometimes CT cabinet) and service panel or disconnect. When concentric knockouts are present and at least one ring remains, a bonding or grounding bushing is required. When all rings have been removed or if you punch your own knockouts (eccentic K.O.s) a grounding locknut is used rather than a bonding bushing. Some engineers will spec bonding bushings on all conduits entering a panel or box through concentric knockouts, but it's rare to see a spec like that. As far as I know, voltage is not an issue on whether bonding bushings are required.
 
 