Question 2 Horizontal Breaker Spaces to 2 Vertical Breaker Spaces

There is an opportunity to weld some hot metal in my garage, if I can get the 50 Amp Homelite breaker into my 10-year old 200-amp panel.

The dilemma with installing the breaker and plug is caused by my lack of open slots in the panel. There are only 2 left. And, of course the slots are horizontal when I need vertical slots.



Things may be able to be moved around. But, I don't know about adjusting panel breaker positions. So, I'm asking the experts.

 
  #2  
Old 06-03-15, 10:47 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Yes, you can do that. You can wire nut extensions on to the wires if needed.
 
  #3  
Old 06-04-15, 06:17 AM
P
Member
Thread Starter
Join Date: May 2015
Location: United States
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thumbs up Thank you for confirmation

One of my YouTube instructors, AskMeDIY talked about not putting wire nuts in panel boxes. I wasn't sure whether I would need to try my best to stretch the lines, from their origin/appliance, to get several inches of wire to swap things around. My home is in the county in North Alabama, so I don't have any codes or need a permit. But, I don't want to botch anything to risk the safety of my home.

Name:  Open_Panel_Musical_Breakers.jpg
Views: 819
Size:  36.1 KB

Name:  Ugg1.jpg
Views: 420
Size:  30.9 KB

Name:  Ugg2.jpg
Views: 320
Size:  34.3 KB

Name:  Ugg3.jpg
Views: 513
Size:  43.1 KB

Name:  Ugg4.jpg
Views: 303
Size:  32.4 KB

Name:  Ugg5.jpg
Views: 317
Size:  33.5 KB

Name:  Ugg6.jpg
Views: 341
Size:  41.1 KB

Name:  Ugg7.jpg
Views: 336
Size:  39.9 KB

Name:  Ugg200.jpg
Views: 329
Size:  37.0 KB
 
  #4  
Old 06-04-15, 06:30 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,976
Received 194 Upvotes on 170 Posts
There is no issue with wire nuts in a panel to extend a few wires.
 
  #5  
Old 06-04-15, 08:28 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
AskMeDIY talked about not putting wire nuts in panel boxes.
He may have been Canadian. I have read they don't allow splices in the panel.
 
  #6  
Old 06-04-15, 06:24 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,871
Received 185 Upvotes on 166 Posts
And, of course the slots are horizontal when I need vertical slots.
Why would you need vertical slots?
 
  #7  
Old 06-04-15, 06:41 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,976
Received 194 Upvotes on 170 Posts
Trying to add a 2 pole 50 for a welder.
 
  #8  
Old 06-04-15, 06:50 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,871
Received 185 Upvotes on 166 Posts
His panel has horizontal slots to match the busbars, why does he need vertical slots?
 
  #9  
Old 06-04-15, 06:55 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,329
Received 877 Upvotes on 740 Posts
He needs two spaces for a two pole breaker. I would just move one 20 amp single pole breaker and then just bump the 30 amp breaker on the right down one slot.
 
  #10  
Old 06-04-15, 06:56 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes on 30 Posts
I don't see any bus stabs below the already fitted circuit breakers in the pictures. Some panel covers have more "twist-outs" than there are bus spaces for circuit breakers. Maybe there ARE stabs and I just can't see them due to the angle of the camera and the lack of light.
 
  #11  
Old 06-04-15, 07:00 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,329
Received 877 Upvotes on 740 Posts
I though the same thing Furd, but if you look at the first picture of the panel cover off, I think I can see some buses there.

22" monitor FTW
 
  #12  
Old 06-04-15, 07:10 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes on 30 Posts
Maybe, and maybe it is just a bus assembly mounting screw. Need a better picture taken on the same level (or lower) of the suspected stabs.
 
  #13  
Old 06-04-15, 08:26 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Name:  Ugg5.jpg
Views: 327
Size:  51.0 KB
.
 
  #14  
Old 06-04-15, 09:27 PM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,499
Received 92 Upvotes on 84 Posts
Separate issue - Is that a green bonding screw installed?
 
  #15  
Old 06-05-15, 01:40 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,976
Received 194 Upvotes on 170 Posts
I think I see there bond screw on the left bus. If so it should be removed.
 
  #16  
Old 06-05-15, 07:07 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,329
Received 877 Upvotes on 740 Posts
If the main breaker in the panel is the first overcurrent device the bond screw should be installed. The ground wire in the SE cable has me a little confused.
 
  #17  
Old 07-11-15, 05:09 AM
P
Member
Thread Starter
Join Date: May 2015
Location: United States
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Question Space for Upgrade?

Here are the pics of the space I'm hoping will allow expansion, to make room for the two pole 50-amp breaker. Thank y'all for all of the advice and the time you took to analyze my predicament.

[img="Name:  FullSizeRender (55).jpg
Views: 265
Size:  44.2 KB"]

Name:  FullSizeRender (57).jpg
Views: 256
Size:  44.0 KB

Name:  FullSizeRender (53).jpg
Views: 277
Size:  37.9 KB
 
  #18  
Old 07-11-15, 07:51 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,329
Received 877 Upvotes on 740 Posts
Yes, you can move the two single pole breakers as you proposed to make room for the two pole 50 amp breaker. If needed the wires can be spliced if they are to short to reach the new breaker locations.
 
  #19  
Old 07-12-15, 07:19 AM
P
Member
Thread Starter
Join Date: May 2015
Location: United States
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thumbs up Success

The expansion was successful. The two pole 50 amp isn't wired up, yet. But, the 20 amp Kitchen outlets and Washing Machine outlet breakers work just as before and the 50-amp breaker is in its new space.

The advice received saved me lots of money and I certainly appreciate it! It's over 100 degrees here, so I found time to work on it before dawn and spare my family from sweating it out while the main breaker was off.

After realizing my welder power cord is only 6ft and the leads for ground are 6ft, I've decided not to install the welder plug directly beneath the panel. But rather, I'll head back to my local Supply store for a longer section of wire, 30 ft instead of the current 6ft on-hand, to route the plug near the garage entry. That would provide welding capabilities outdoors or inside. And, I'll run the cable up through the attic and behind the drywall.

Xtreme 4x4 makes it look easy to do the welder power supply, min. 10:25 to 15:35. But, that's why Ian Johnson, the show's host, was born for television and metal fab and my 9 to 5 is at a desk. All in all, it is straight forward and as long as safety is top priority, then it is a job that I would rarely discourage.

Name:  FullSizeRender (69).jpg
Views: 268
Size:  35.6 KB

Name:  FullSizeRender (68).jpg
Views: 275
Size:  34.4 KB

Name:  FullSizeRender (67).jpg
Views: 243
Size:  40.4 KB

Name:  FullSizeRender (66).jpg
Views: 256
Size:  29.2 KB
 
  #20  
Old 07-12-15, 07:52 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Good job. Thanks for letting us know.
 
 