Acceptable Wiring Size For Service To Detached Garage

Reply

  #1  
Old 06-07-15, 08:02 AM
Member
Thread Starter
Join Date: Jun 2015
Posts: 2
Received 0 Votes on 0 Posts
Acceptable Wiring Size For Service To Detached Garage

Hello everyone. I recently had a new concrete driveway poured and during site prep the contractor broke and repaired (spliced) a #2 AWG wire that was used to service my detached garage. After a heavy rain the splice failed and as a remedy the contractor wants to run wire around the back side of my house through the front yard and then to the detached garage for a total distance of 280 feet. He wants to run aluminum wire. I have a 100 Amp service in the detached garage. I asked him about the additional distance that would be required to service the detached garage and he said that number 2 AWG was good for up to 500 feet. Does this sound correct? Thank you in advance for your replies. Andy
 
Sponsored Links
  #2  
Old 06-07-15, 08:41 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
First question is why do you have a 100 amps to the garage? You could run a whole house on that. A 100 amp subpanel does not mean you need a 100 amp feed. Do you have a large welder, compressor, and electric heat, maybe an electric car charging station in the garage?
 
  #3  
Old 06-07-15, 09:00 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,978
Received 35 Votes on 30 Posts
Voltage drop is dependent on the load as well as the distance and would factor heavily in determining the correct wire size.
 
  #4  
Old 06-08-15, 08:21 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
It also depends on which code version your local area is following. The latest codes do not allow 100A on #2 aluminum for any distance. In prior versions, the distance as well as the load is important with a recommendation of not exceeding 3% voltage drop. For a full 100A load, that means you would need aluminum wire no smaller than #4/0 for a 280' distance. Whether or nor you need to support the full 100A is based on what machines you use in the garage and what you can negotiate with the contractor. In either case I think the 500' distance is absurd, and certainly is not based on the NEC.
 
  #5  
Old 06-09-15, 06:14 PM
Member
Thread Starter
Join Date: Jun 2015
Posts: 2
Received 0 Votes on 0 Posts
Thanks for the replies all. I plan on brewing beer in the garage. I will never use all of the 100 amps but I also have a small apartment above the garage. The line is buried now so the point is probably mute at this time. I guess to know for sure I should measure the voltage drop at the garage breaker box????
 
  #6  
Old 06-10-15, 05:40 AM
Member
Join Date: Mar 2010
Location: USA
Posts: 3,679
Received 30 Votes on 29 Posts
What was actually installed? Number 2 aluminum is not going to carry very much current 560 feet. When the apartment is occupied you might not be able to brew any beer in the garage below.

You would need to do a load analysis (the NEC gives the rules) for the garage and for the apartment to figure out the amperes (or watts) needed out there. Then use wire resistance charts (available using Google) to come up with the minimum conductor size for the feed. Included in a load analysis would be the machines you plan to use in the garage.
 
  #7  
Old 06-10-15, 08:53 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,223
Received 38 Votes on 30 Posts
he said that number 2 AWG was good for up to 500 feet.
That statement alone tells me you need an electrical contractor to do this work and not a concrete contractor.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: