60 amp feeder to 100 amp panel
Hey folks, I am needing help
I just bought some RV property with the original 60 AMP service panel (and glass breakers). The country installed a a new meter last year. The panel and outlets have been flooded and they just need replaced
So, eventually, when I have the money, I will have the PUD move my electric back up to the street. In the mean time I want to upgrade my panel and outlets...
My question is this: Somebody gave me a 100 amp panel, can I use this panel? WIll that feeder to the meter be strong enough? If not, can I use it anyway and just run up to 60 amps on that panel until I change that feeder.
I am hoping that wire to the meter is plenty strong, but this is all new to me
I just bought some RV property with the original 60 AMP service panel (and glass breakers). The country installed a a new meter last year. The panel and outlets have been flooded and they just need replaced
So, eventually, when I have the money, I will have the PUD move my electric back up to the street. In the mean time I want to upgrade my panel and outlets...
My question is this: Somebody gave me a 100 amp panel, can I use this panel? WIll that feeder to the meter be strong enough? If not, can I use it anyway and just run up to 60 amps on that panel until I change that feeder.
I am hoping that wire to the meter is plenty strong, but this is all new to me
#5
My question is this: Somebody gave me a 100 amp panel, can I use this panel? WIll that feeder to the meter be strong enough?
#6
Member
Thread Starter
Join Date: May 2015
Location: USA
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I understand what you are saying, I communicated poorly. My concern was this: Is the wiring coming down to my meter enough to support 100 amps? Or would itr just be enough to support the original 60 amp service
#7
Is the wiring coming down to my meter enough to support 100 amps?
#8
Usually that wire is owned by the power company, so it is not the property owner's concern. You tell them how much power you actually use (not necessarily the same as the service or panel size), and they select and install an appropriate wire.
#9
Member
Thread Starter
Join Date: May 2015
Location: USA
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Yes that is what I thought, however the man at the PUD seemed to think I was responsible for that...Everybody else told me what you are saying, everything below meter is mine...Well maybe I will do the 100 amp hook up an hope it works, if not, put in on the PUD since they give me varying responses
#10
Who is the owner of the wire will depend on local rules. In my location, an underground feeder to the line side of the meter is the power company's and is the overhead the drop. After were the overhead wires connect to the building/mast is the property owners. Normally anything after the meter is the property owners responsibility.
This is not a good option and a good way to cause a fire. You need to look at the wire size and confirm that it is AT LEAST #4 copper or #2 aluminum.
Well maybe I will do the 100 amp hook up an hope it works
#11
You could back feed the 60 amp breaker until you can upgrade the service. You would need as breaker hold down installed on the 60.
#12
Member
Thread Starter
Join Date: May 2015
Location: USA
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The PUD said it should be a number 2 overhead triplex, if that is the case he said that should support 100 no problem and probably 200...Now I have to figure it out...Also, he said 100 amp is close enough to 60 regardless of wire but I do not believe that. SOunds like a hazard to me
#14
The triplex sizes fall under a different set of sizing rules. You need the correct size from the weatherhead to the meter and meter to panel to upgrade to 100 amps.
#15
PCBoss pointed out:
Just to clarify in my original replies that is what I was reffering to not the drop.
You need the correct size from the weatherhead to the meter and meter to panel to upgrade to 100 amps.
#16
#2 is OK, but that is their wire. You need to look at the wire size from the attachment point to the line side of the meter, and the wire on the load side of the meter to the main panel. If all that is #2 AL or #4 copper, then it would be OK for 100 amps. Power companies today will normally run 200 amp wire regardless of the service size to a house unless it over 200 amp. Keeps everything standard.