Can over-size wire?

Reply

  #1  
Old 06-13-15, 07:55 AM
Member
Thread Starter
Join Date: Oct 2001
Location: USA
Posts: 878
Can over-size wire?

I am going to install a new bath exhaust fan. I will be taking off from an existing receptacle on a 15A circuit. I have a bunch of 12/2 wire that I would like to use. Is that to code (the wire would be oversized) or do I need to buy some 14/2?
 
Sponsored Links
  #2  
Old 06-13-15, 08:21 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,212
Yes, you can use 12-2 NM-B cable on a 15 amp circuit.
 
  #3  
Old 06-13-15, 11:02 AM
Member
Thread Starter
Join Date: Oct 2001
Location: USA
Posts: 878
Thanks for the response!

I suspected I could, but wanted to be sure. If I were building a new home, every receptacle would be 20A.
 
  #4  
Old 06-13-15, 12:16 PM
Gunguy45's Avatar
Super Moderator
Join Date: Dec 2007
Location: USA
Posts: 20,849
Unless I'm mistaken, it's the other way around where you can have problems. Tapping off a 14Ga supply with 12 is bad. I'll be corrected if I'm wrong.
 
  #5  
Old 06-13-15, 12:18 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,631
every receptacle would be 20A
By USA code (Canada varies) the receptacles can be rated at 15 amps on a 20 amp circuit so long as there are two or more places to plug in. A single duplex receptacle meets that requirement.The 15 amp receptacles are rated 20 amp pass through.
 