power to main breaker but not condenser disconnect

My outdoor condenser is not working. The capacitors, contactor and fuses all tested fine. There is 240 from the main breaker, but not at the disconnect. What could be wrong in between, and how would I go about fixing this?
 
  #2  
Old 06-20-15, 12:46 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
What are your voltage readings at the disconnect for each hot to ground on the line side?
 
  #3  
Old 06-20-15, 12:49 PM
S
Member
Thread Starter
Join Date: Jun 2015
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for responding! Voltage is at zero on both sides of the disconnect.
 
  #4  
Old 06-20-15, 12:55 PM
S
Member
Thread Starter
Join Date: Jun 2015
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
There is zero voltage for each leg at disconnect, but I'm getting 240 from the main breaker. I don't understand how this could be
 
  #5  
Old 06-20-15, 02:32 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
How are you measuring voltage. It almost sounds like you are using a non contact tester. That won't work. You need to use a multimeter to test each leg to ground.
 
  #6  
Old 06-20-15, 03:17 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 36,607
Upvotes: 0
Received 9 Upvotes on 8 Posts
While you do that, check between the breaker location and the disconnect location for any junction boxes in the line. It happens.
 
  #7  
Old 06-20-15, 03:37 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,816
Received 3,922 Upvotes on 3,518 Posts
You're checking at the "main breaker" ??

You should be checking at a 2P30A or similar breaker.
 
  #8  
Old 06-20-15, 03:41 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 36,607
Upvotes: 0
Received 9 Upvotes on 8 Posts
Wow, Pete, that went right over my head. Good catch.
 
  #9  
Old 06-20-15, 06:21 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,977
Received 194 Upvotes on 170 Posts
You need to check the breaker terminals that feeds te circuit, not the main.
 
 