2 Heaters on Dual Pole GFCI Breaker


  #1  
Old 06-22-15, 03:59 PM
T
Member
Thread Starter
Join Date: Jan 2015
Posts: 22
Upvotes: 0
Received 0 Upvotes on 0 Posts
2 Heaters on Dual Pole GFCI Breaker

Hey all,

I have a 12-3 line MWC running out of my sub panel.
If I have two outdoor heaters at 120v rated at 1500w (12.5 amps) each, can I run each on one leg of the 20 dual pole GFCI Breaker?

Will each leg provide 20 Amps so that the CB will not trip, or is it a combined 20amps?

If not, any suggestions on how to wire without swapping out the 12-3 line (UF fed underground)?
 
  #2  
Old 06-22-15, 04:56 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Each 120 circuit is 20 amps.
 
  #3  
Old 06-22-15, 05:23 PM
T
Member
Thread Starter
Join Date: Jan 2015
Posts: 22
Upvotes: 0
Received 0 Upvotes on 0 Posts
That sounds like good news!

To play devils advocate though....Will the potential 25 amps(12.5 +12.5) on the shared neutral to the GFCI breaker not trip the breaker? At that point does that mean the breaker is actually allowing up to 40 amps to pass through it before tripping?
 
  #4  
Old 06-22-15, 05:39 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 65,100
Received 3,983 Upvotes on 3,575 Posts
When you run a circuit like that..... the loads technically get connected between the red and black wire so that the neutral only carries the imbalance.

There will never be more than a 20A load on the neutral wire.

Since you are running identical loads..... there will be 0A on the neutral if both heaters are running. If only one heater is running there will be 12.5A on the neutral.

Name:  mwc.jpg
Views: 247
Size:  7.7 KB

The blue squares are the heaters.
 
  #5  
Old 06-22-15, 07:12 PM
T
Member
Thread Starter
Join Date: Jan 2015
Posts: 22
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks so much for the diagram, it jogged my memory, I am SOLD!

Apparently 1 year ago me knew what I was doing, and now, for some reason when I'm about to put in the heaters I was doubting myself.

Thanks again.
 
 