Hardwiring a range
#1
Member
Thread Starter
Join Date: Oct 2007
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Hardwiring a range
Hi - i want to hardwire a new range (which states you can do a 3-wire conduit installation). i live in a old house and i have a dedicated circuit which has a large, heavy, black cloth covered cable running out of it with 3 separate cloth covered wires which are a collection of wires braided together and covered again with black cloth, white cloth and the ground is uncovered. The older range was hardwired directly into the back with this. Here's a link to the photo: https://www.dropbox.com/s/uu0y76q1lq...20.24.jpg?dl=0

i'm used to using romex with a single wire - so this looks like it's hard to work with and i want to make sure i connect it correctly. The range directions just show a single cord running up into the terminal opening.
Someone suggested that i get 3 terminal lug - single conductors to attach the wires to and then attach to the back of the stove.
Does all this sound like i am heading in the right direction?
Thanks!

i'm used to using romex with a single wire - so this looks like it's hard to work with and i want to make sure i connect it correctly. The range directions just show a single cord running up into the terminal opening.
Someone suggested that i get 3 terminal lug - single conductors to attach the wires to and then attach to the back of the stove.
Does all this sound like i am heading in the right direction?
Thanks!
Last edited by PJmax; 06-30-15 at 05:57 PM. Reason: added pic from link
#2
Your existing wiring is OK and would be grandfathered in as long it is able to handle the load of the new range.
Likely the new range is intended to be cord connected and that is how I would suggest to wire it. Get a 3 wire range cord and connect it following the instructions of your range. Then get a surface mounted, 3 wire range receptacle and connect the house wiring to that. It will be much easier than trying to wire the old wire directly to the range.
Likely the new range is intended to be cord connected and that is how I would suggest to wire it. Get a 3 wire range cord and connect it following the instructions of your range. Then get a surface mounted, 3 wire range receptacle and connect the house wiring to that. It will be much easier than trying to wire the old wire directly to the range.
#3
I too vote for adding a cord and a new receptacle. The cord will serve as the disconnect and will hold up better when moving the range to clean.
#4
Member
Thread Starter
Join Date: Oct 2007
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks for the replies!
The one issue with adding a range receptacle is that the wall behind the range is double brick. the cord is coming up through the basement in through the floor - so i'm not sure if it is acceptable to have a receptacle installed in a kitchen floor??
Curious... what type of wiring is this? approx. how old?
Also the circuit board has a double circuit (2 connected together) with 2 40 amp circuits for the range -
The one issue with adding a range receptacle is that the wall behind the range is double brick. the cord is coming up through the basement in through the floor - so i'm not sure if it is acceptable to have a receptacle installed in a kitchen floor??
Curious... what type of wiring is this? approx. how old?
Also the circuit board has a double circuit (2 connected together) with 2 40 amp circuits for the range -
#5
Yes, surface mounted receptacles can be mounted on the floor. This is what you need: Leviton 50 Amp Thermoplastic Power Single Outlet - Black-R50-05050-000 - The Home Depot
That is a 2 pole, 240 volt, 40 amp circuit.
It appears to be early non-metallic cable, likely original to the house. How old is the house?
Also the circuit board has a double circuit (2 connected together) with 2 40 amp circuits for the range -
what type of wiring is this? approx. how old?
#6
Member
Thread Starter
Join Date: Oct 2007
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
the house was built in 1885....old!
Actually - there is 4.5 feet of extra cord coming up from the basement - so if there's a need to move the range, there's plenty of extra.... is it still advisable to do the receptacle instead of the hardwiring?
One other question.... is it a good idea to wrap the cord as it is now with electrical tape??
thanks again for your expertise!!!!
Actually - there is 4.5 feet of extra cord coming up from the basement - so if there's a need to move the range, there's plenty of extra.... is it still advisable to do the receptacle instead of the hardwiring?
One other question.... is it a good idea to wrap the cord as it is now with electrical tape??
thanks again for your expertise!!!!
#7
The old Romex is probably from the 1940s or 50s. If the wire insulation under the wound fiber string is more like plastic it's post-1950, if it's rubber it is probably 1940s, possibly even 30s but that wire is generally wrapped in natural fiber like cotton. If it was my house, I would replace the cable with modern #8-3/g cable.
Yes the receptacle and range cord is still a better idea than hardwiring.
Yes the receptacle and range cord is still a better idea than hardwiring.
#9
The old Romex is probably from the 1940s or 50s.
#10
I will jump in an say based on the age that is SE cable and I would also replace it because of age.
#11
Can you see the entire cable run in the basement? If so you might want to replace it.
If not, I would suggest pulling up the slack of the old cable and strip it so you have a new, clean section of cable.
BTW - If that wire is aluminum, you should also use some anti oxidation paste.
If not, I would suggest pulling up the slack of the old cable and strip it so you have a new, clean section of cable.
BTW - If that wire is aluminum, you should also use some anti oxidation paste.
#12
Member
Thread Starter
Join Date: Oct 2007
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
the cable runs into a large junction box which i haven't opened - and then runs directly to the circuit box.
guess i should look in the large junction box....and see what's happening in there.
guess i should look in the large junction box....and see what's happening in there.
#13
Member
Thread Starter
Join Date: Oct 2007
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
just opened the junction box and took a pic.... the cable from the kitchen goes in and it looks like someone at some point added wire nuts - and lots of electrical tape;-) but it looks like it is just extending the run - the cable comes out of the junction box and then runs out to the main box.
how difficult is it to re-wire to the main box?
pic: https://www.dropbox.com/s/7ka5jzy996el32b/2015-07-01%2012.05.31.jpg?dl=0
how difficult is it to re-wire to the main box?
pic: https://www.dropbox.com/s/7ka5jzy996el32b/2015-07-01%2012.05.31.jpg?dl=0

Last edited by ray2047; 07-01-15 at 10:20 AM.
#14
Definitely best to go with a new code compliant 4-wire circuit.
Do you have an unfinished basement or crawl space below? Or do you have an unfinished attic above?
how difficult is it to re-wire to the main box?
#15
You would parallel the path of the existing cable with the new cable. Leave out the junction box in the middle. 6-3 w ground NM-B and a surface mount receptacle would work.