Bad circuit breaker or wiring problem ?
While extending a 15a circuit to include a new receptacle, a wire nut came off, created a short and tripped the breaker. When I reset the breaker lights on the circuit began to flicker occasionally and then go off. When I checked on the breaker again it was not tripped but I flipped it off and back on anyway. Now that circuit will stay live for a while then go out then go live again but the breaker does not trip. What's going on? Thanks.
You have a loose connection someplace on that circuit. You will need an electrical meter (analog preferably) to track it down, but if your lucky, you might be able to just see it. You will have to start removing devices (switches, lights, receptacles) on that circuit and inspecting the connections. If you have any back stabbed devices I recommend moving the wires to the side screw terminals.
With power removed from the circuit, remove all receptacles and light switches on that circuit and take the stab back connections and replace them under the corresponding screw heads. This is the most frequent cause of flickering lights that I have found.
The symptoms sound a lot like what happens eventually with all Zinsco breakers or Zinsco style Sylvania breakers.
Bingo. It's an old Zinsco. Do I need a new panel? And I forgot to add this important bit of info: my funky old house has Romex, sheathed cable and K & T. I have been replacing the K & T little by little.
How much is a new 200a panel with 14 circuits gonna cost me? MANY thanks.
PS...
Does Zinsco panel need a particular style breaker? At least some of the ones in place are Westinghouse. I will install a new circuit breaker until I can get an electrician to come out to talk about a panel upgrade (which could be weeks in my town).
You don't necessarily need a 200A panel (150A and 100A are common), but a new panel is a good idea. The size is established with a "demand load calculation". Zinsco panels are known to have a much higher failure rate than other panels of similar age.
It's very hard to give estimates over the Internet due to significant variation in labor price and permit fees. Something on the order of $1,500 to $2,500 is reasonable for an uncomplicated service replacement, which includes a new main panel, new grounding system, new conduits and service entrance wires, possibly a new meter base and mast for an overhead service. That generally does not include any structural changes or speciality equipment that might need to occur if your situation is not a straightforward replacement of old equipment. Get a few estimates from reputable contractors and proceed from there.
follow up
Veteran electrician (71!) says cost of replacing Zinsco aluminum buss bars with copper and installing three new breakers will be $1100. Seems high since it ought to be a two hour job. Or am I wrong?
He also tells me that the cost of putting in a whole-house surge protector would be $550.
*The other source of breakers is used ones and the original problem was the breakers not the bus bars.
Everything you guys say makes very good sense to me, but electrician said new panel would be $3600 and I'd be without power for two or three days. Talking to another guy this afternoon.
In my southern CA town it is very hard to hire a tradesman because there are many rich people and the tradesmen are used to making top dollar so middle class folks get overcharged. Or if you make a deal and set a date, the tradesman is likely to call that morning and say he needs to postpone (because he got a job working for the 'carriage trade' and wants to put your little project on hold. Never mind that you took a day off work to wait for him at the house.) This has happened to me three or four times.
Again, I'm grateful to you all.
In my location we do everything, cut the power, pull the meter, do the swap, and reconnect with some temporary splices and reinstall the meter. Power company doesn't show up to finish splice and put their seal on until after the inspector signs off on it, which can be days later.
#21
A simple panel change requires no temporary connections. Pull the meter, change the panel and reinstall the meter. Presto....done.....1/2 day at most. This does however require a permit and there will need to be an inspection at some point, but that can be scheduled with the AHJ. Then the POCO will come rerseal the meter once they receive the wiring approval from the AHJ.
You are definitely talking to the wrong guy.
#22
Typically when we changing the panel, we are also required to change the meter to one that has a bypass handle. Otherwise the power company will not reconnect it. Also many cases the mast needs to be replaced.
#23
The requirement for a lever bypass meter socket seems to be moving across the country, they are required in my area now for a new service or for a complete service replacement. Just a panel change though doesn't require a new meter socket here. A lever bypass meter socket typically costs about $100 more than the older traditional sockets. An estimate of $3600 to just change a panel is still way out of line.
#24
Because I know ya'll are losing sleep over my situation, I thought I'd better report.
Second (young) electrician came out and gave me an estimate of $2000 for putting in a new panel (inc. permit). He said he thought the mast would not have to be moved, but if it did, there would be no extra charge. I have a two-year-old digital meter, so I won't need a new one. Don't know about the handle requirement around here, but of course I'm going with the new panel per this forum's good advice.
BTW, I found the first guy - the vet - via word of mouth. The young guy I found on Yelp. He had many glowing reviews.
Again, thanks to all.
#26
He said I'd be without power for 'a couple of hours.' Can't get to the job for three weeks though. He asked me what I do for a living and I told him I am a school teacher. He said 'you seem to know a bit about wiring.' No, but thanks to ya'll I can ask intelligent questions (mostly). Don't forget to ask your satisfied customers to review you on Yelp.
#27
$2000 sounds like a good price.