Shared Neutrals and Double Pole Breakers


  #1  
Old 06-30-15, 08:25 PM
S
Member
Thread Starter
Join Date: Jan 2012
Location: United States
Posts: 84
Upvotes: 0
Received 0 Upvotes on 0 Posts
Shared Neutrals and Double Pole Breakers

I posted a few weeks back regarding shared neutrals and came to learn the breakers need to be tied. I ended up using a double pole 20a breaker on the advice of the local electrical supply store (that isn't a Lowes or HD .

If I can make sense of what branches are sharing neutrals and 'tie' the breakers by using double pole breakers, do I use 20a double pole to replace the two 20a single poles? Or do I use a 40a double pole?
 
  #2  
Old 06-30-15, 08:39 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,139
Received 3,619 Upvotes on 3,245 Posts
The amperage posted on a breaker is the actual circuit amperage. They don't get added because it's a double breaker.

You use a 2 Pole 20A breaker.
 
  #3  
Old 07-01-15, 05:15 AM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,422
Upvotes: 0
Received 261 Upvotes on 238 Posts
One double wide double pole 20 ampere breaker is used with:
One 20 amp 240 volt circuit, or,
A multiwire branch circuit (with shared neutral) that provides two allotments of up to 20 amps at 120 volts each, or,
(not frequently seen) Two independent 20 amp 120 volt circuits.
 
  #4  
Old 07-01-15, 06:43 AM
Handyone's Avatar
Member
Join Date: Aug 2000
Location: U.S.
Posts: 4,807
Upvotes: 0
Received 0 Upvotes on 0 Posts
If I can make sense of what branches are sharing neutrals
A good place to start looking for MWBC's is the kitchen.
The disposer and dishwasher are often shared. The 2 small appliance circuits are often shared.

Another possible place is an above the range microwave sharing with something else.

If you look in the panel for #12 red wires, you can trace them to where they exit the panel via a 12/3 cable, and then trace the black wire back to it's respective breaker.
 
  #5  
Old 07-01-15, 07:54 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,827
Received 178 Upvotes on 161 Posts
I ended up using a double pole 20a breaker on the advice of the local electrical supply store
That is one way to tie the circuits together and the least expensive, but I find it preferable to use a handle tie with two 1 pole breakers. With a 2 pole breaker if you have a problem with one of the circuits, the 2 pole breaker trips and you don't know without further testing which circuit caused the problem. When using a handle tie, only the breaker with the problem will trip. The code requires common disconnect when manually turning off the circuits, but the code does not require common tripping.
 
 