Outdoor GFI tripping under load

OK everyone I am stumped with my GFI curcut and need some help which is greatly appreciated.

Background into the circuit

I installed a dedicated outdoor curcut for my outdoor needs. It is 15 amp originally with the first outlet being a GFI outlet and the remaining outlets in my front yard being lights and a sprinker timer. The lines are outdoor wire that can be put underground. Over the years I have had to replace the GFI outlet I would say every three years as it started to trip more often.

So last month I wanted to fix the problem for ever so I installed a GFI breaker in the curcut box for this outdoor circuit removing the GFI outlet in the first box.

This is when my current problem started. The GFI breaker when in fine and tests OK when I manually trip it at the panel or out an outdoor plug. I can place a small load ( my cordless charger wihich only has a single light to it getting power) but under any kind of load the GFI breaker in the box trips. I have tried various loads with the same result and nothing else in plugged into the curcuit. Any ideas?

Thanks in advance for the help.
 
Sponsored Links
  #2  
Old 07-04-15, 04:27 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,946
Received 31 Votes on 27 Posts
Gfi's do not trip from overloads. They trip because there is an imbalance between the outgoing and return current. It sounds like it is leaking somewhere . What materials did you use and how deep was it buried ?
 
  #3  
Old 07-04-15, 05:58 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Location: USA
Posts: 4,032
Received 18 Votes on 18 Posts
Does it trip when you plug something into one of the other outlets or when the timer only comes on?
Geo
 
  #4  
Old 07-04-15, 08:03 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,210
Received 379 Votes on 356 Posts
Moving the GFI from the receptacle to the panel didn't address your original problem which is like PC said.... a leak to ground.... and most likely underground.

If I was troubleshooting the circuit I would disconnect the white and black wires at the panel.
I would take an ohmmeter set to a high scale and check from white to ground and black to ground. There should be no indication of continuity. Any leakage to ground from either wire will cause the GFI to trip prematurely.
 
  #5  
Old 07-04-15, 08:39 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,051
Received 26 Votes on 20 Posts
Gfi's do not trip from overloads.
In this case it could because the GFCI receptacle was removed and replaced with a GFCI circuit breaker. But, I think you are right, the OP is getting leakage in the circuit causing a ground fault.
 
  #6  
Old 07-06-15, 10:12 PM
Member
Thread Starter
Join Date: Sep 2014
Location: USA
Posts: 12
Received 0 Votes on 0 Posts
Thank you everyone for your responses. Sorry for my slow response as I don't normally post a question then not respond although on the 4th of July my next door neighbor have an accident and was killed. Not fireworks but tree related and breaks our hearts as he had young family.

PJ I will try your idea and report back. Many thanks but if it is leaking it going to be a nightmare
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: