Surge Protection

To hi-jack this thread-

If a home has a non-grounded wiring system (1952) and surge protector(s) will not protect components without a ground, will a power-up with a surge protection device @ the new panel possibly prevent outside power surges until the home is rewired ($$$)?
 
Sponsored Links
  #2  
Old 07-07-15, 08:35 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,280
Received 43 Votes on 35 Posts
will a power-up with a surge protection device @ the new panel possibly prevent outside power surges until the home is rewired
What is a power-up? You cannot prevent power surges from outside the home, but a whole house surge suppression device, properly installed at the service panel, will prevent them from causing damage.
 
  #3  
Old 07-07-15, 05:05 PM
KULTULZ's Avatar
Member
Thread Starter
Join Date: Jan 2008
Location: USA
Posts: 28
Received 0 Votes on 0 Posts
What is a power-up?
Service upgrade, i.e. 100A to a 200A service (breaker panel).

The home is wired 2-wire with no ground presently.

Will a service/panel upgrade (with proper grounding) allow a surge protection device @ service entry to provide electronic device(s) protection within the home from outside surges until the home can be rewired to three wire service?

THANX!
 
  #4  
Old 07-07-15, 06:28 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Will a service/panel upgrade (with proper grounding) allow a surge protection device @ service entry to provide electronic device(s) protection within the home from outside surges until the home can be rewired to three wire service?
No need to upgrade your current service. It should already be grounded and will with a whole surge protector provide the same protection as a new service.

I think you are confusing GEC* and EGC**. Your receptacles don't have EGC which is needed for individual receptacle protection but whole house relies on GEC. Any panel from even 60 years ago should have GEC and bonding***. Even if not it can be easily added.

*GEC, Ground Electrode Conductor, is for atmospheric charge protection. It consists of one are more ground rods and or a connection to the water pipes if they are metal.

**EGC, Equipment grounding conductor, is a low resistance to clear shorts to the metal of equipment or fixtures by tripping a breaker (or fuse). It can be used as a path for localized surged protection because it is connected to the GEC at the main panel (or in some case meter).

***Bonding is connecting metal plumbing to the GEC and EGC at the main panel to prevent a voltage difference between neutral or ground and the pipes.
 
  #5  
Old 07-07-15, 07:34 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,996
Received 39 Votes on 34 Posts
The size of the service has no bearing in this case. A larger service just allows more loads to be used at the same time.
 
  #6  
Old 07-08-15, 01:08 AM
KULTULZ's Avatar
Member
Thread Starter
Join Date: Jan 2008
Location: USA
Posts: 28
Received 0 Votes on 0 Posts
No need to upgrade your current service. It should already be grounded and will with a whole surge protector provide the same protection as a new service.
That's what I needed to know.

The upgrade is planned as to allow more capacity in the house as it is rewired and new circuits added.

I appreciate it gentlemen...
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: