Surge Protection
To hi-jack this thread- 
If a home has a non-grounded wiring system (1952) and surge protector(s) will not protect components without a ground, will a power-up with a surge protection device @ the new panel possibly prevent outside power surges until the home is rewired ($$$)?

If a home has a non-grounded wiring system (1952) and surge protector(s) will not protect components without a ground, will a power-up with a surge protection device @ the new panel possibly prevent outside power surges until the home is rewired ($$$)?
#2
will a power-up with a surge protection device @ the new panel possibly prevent outside power surges until the home is rewired
#3
What is a power-up?
The home is wired 2-wire with no ground presently.
Will a service/panel upgrade (with proper grounding) allow a surge protection device @ service entry to provide electronic device(s) protection within the home from outside surges until the home can be rewired to three wire service?
THANX!
#4
Will a service/panel upgrade (with proper grounding) allow a surge protection device @ service entry to provide electronic device(s) protection within the home from outside surges until the home can be rewired to three wire service?
I think you are confusing GEC* and EGC**. Your receptacles don't have EGC which is needed for individual receptacle protection but whole house relies on GEC. Any panel from even 60 years ago should have GEC and bonding***. Even if not it can be easily added.
*GEC, Ground Electrode Conductor, is for atmospheric charge protection. It consists of one are more ground rods and or a connection to the water pipes if they are metal.
**EGC, Equipment grounding conductor, is a low resistance to clear shorts to the metal of equipment or fixtures by tripping a breaker (or fuse). It can be used as a path for localized surged protection because it is connected to the GEC at the main panel (or in some case meter).
***Bonding is connecting metal plumbing to the GEC and EGC at the main panel to prevent a voltage difference between neutral or ground and the pipes.
#5
The size of the service has no bearing in this case. A larger service just allows more loads to be used at the same time.
#6
No need to upgrade your current service. It should already be grounded and will with a whole surge protector provide the same protection as a new service.
The upgrade is planned as to allow more capacity in the house as it is rewired and new circuits added.
I appreciate it gentlemen...