How to replace a standard 5 wire outlet with GFCI?
#1
Member
Thread Starter
Join Date: Aug 2005
Location: Earth
Posts: 102
Received 0 Votes
on
0 Posts
How to replace a standard 5 wire outlet with GFCI?
I want to replace a standard 5 wire receptacle with a GFCI. I purchased a GFCI receptacle. It has a yellow sticker wrapped around the at the top two terminal and says not use it. How do I wire this?
Sponsored Links
#3
I want to replace a standard 5 wire receptacle
It has a yellow sticker wrapped around the at the top two terminal and says not use

Connect the wires of the cable to the next receptacle if you want it to be GFCI protected to the terminals with the tape. The line cable, the one that reads 120 volts black to white goes to the line terminals. (Note: you can not use a non contact tester to determine which cable is hot.)
Terminology note:
the top two terminal
Last edited by ray2047; 07-16-15 at 11:14 PM.
#4
Member
Thread Starter
Join Date: Aug 2005
Location: Earth
Posts: 102
Received 0 Votes
on
0 Posts
Apologize for not explaining clearly.. Yes. 2 white, 2 black and a Neural in the existing outlet which I want to change to a GFCI. Yes the picture you show above is what it says. Also I do not want the next receptacle to be GFCI protected.
#6
Although Pugsi's method is the preferred method of connection you can also connect two wires at each screw location. The yellow tape covering the second set of screw terminals gets left in place.

#9
Member
Thread Starter
Join Date: Aug 2005
Location: Earth
Posts: 102
Received 0 Votes
on
0 Posts
Yes I meant Ground
Thanks you all for the help. Will wire per the above suggestions
Thanks you all for the help. Will wire per the above suggestions
«