Replace 20 amp breaker with 25 amp breaker
Hi all-
Long story short, I have a 20 amp dual pole breaker with 12 gauge wire for central air currently. The a/c unit needs 25 amp. Had a guy out to service the a/c and he was the one who told be that it needed to be 25. He was going to swap out the 20 with a 30 amp until he noticed it was 12 gauge wire. He said he didn't want to run the risk of starting a fire, but that I could go buy a 25 amp and replace it myself no problem. Is this true?
Temporarily Suspended
Wire Capacity Chart
According to a chart on that site, the answer is 23 amps, so I suppose it's close enough. Wait for other answers.
Yes, you can upsize the CB only on dedicated motor circuits, like your a/c. 25A is fine on 12AWG. You may see the mark HACR on the breaker; this means it has a time delay characteristic to accommodate high inrush motor currents, esp. compressors.
Hopefully it is a short run between your panel and the condenser. A long piece of #12 will have a lot of voltage sag/drop on compressor startup.
If the unit is existing and the 20 amp breaker isn't tripping I'd just leave it alone. If this is a new unit, check the data plate for the Minimum Circuit Ampacity (MCA). If it is 20 amps or less, the #12 wire is fine. Then check the Maximum Overcurrent Protection (MOCP) or Max Fuse Size. If it says 25 amps or higher you can change the breaker to 25 amps.
The unit is not new, it's from 2004. A/C tech said the unit needs a 25 amp. I think they just never changed, or upgraded breaker, when they replaced unit. It is tripping. Did it a couple times earlier this year, now more frequent. I guess the compressor is starting to go and when it is starting up it sometimes throws the breaker. He put a hard start kit on the a/c and it hasn't tripped yet, but with a 25 amp it would trip less often because of the spikes when turning on.
25 amps was never considered a standard circuit breaker size and was always available on special order only till the last several years. Since A-C units have gotten so much more efficient and the required amperage has dropped, so has the circuit protection. Now, most supply houses stock the 25 amp breakers. I believe the box stores have also started stocking some of them as well. In your case, I believe I'd use the 30 amp breaker.
So a 30 would be ok with 12 gauge wire?
Ok cool. I thought the 25 amps was the MCA number. I looked at it again and it says "Minimum Supply Circuit Ampacity" 19 / 19 amp. That must be the number you are looking for.