how to run intersystem bond
#1
Member
Thread Starter
Join Date: Nov 2013
Posts: 98
Upvotes: 0
Received 0 Upvotes
on
0 Posts
how to run intersystem bond
Cant get into meter socket or panel to add #6 for intersystem ground... how would you wire it then? On the metallic raceway correct?
Getting #6 on the ground rod would be very unsightly (how would you do so?) The length of the ground wires from the phone and cable company prohibit getting them closer to the ground rod. So the ground block would have to be about 4' from ground level.
Currently both phone and cable have separate straps on the raceway.... done like this on every installation in our area by att and Comcast. I don't think the instersystem blocks are done even on new construction here?
Getting #6 on the ground rod would be very unsightly (how would you do so?) The length of the ground wires from the phone and cable company prohibit getting them closer to the ground rod. So the ground block would have to be about 4' from ground level.
Currently both phone and cable have separate straps on the raceway.... done like this on every installation in our area by att and Comcast. I don't think the instersystem blocks are done even on new construction here?
#2
I'm not sure I understand the question. The intersystem ground bridge is installed on the the GEC (grounding electrode conductors), which is the wire running from the main panel to the ground rod(s). I usually put the bridge about 12" above grade screwed to the house.
The metallic service entrance raceway is a legal point for telecom systems to ground to using an approved strap (looks like plumbing hanger strap).
If you're moving the location of the grounding bridge, you may need to lengthen the ground wires from the phone and cable. Replacing the entire length or an irreversible crimp would be acceptable.
The metallic service entrance raceway is a legal point for telecom systems to ground to using an approved strap (looks like plumbing hanger strap).
If you're moving the location of the grounding bridge, you may need to lengthen the ground wires from the phone and cable. Replacing the entire length or an irreversible crimp would be acceptable.
#3
Member
Thread Starter
Join Date: Nov 2013
Posts: 98
Upvotes: 0
Received 0 Upvotes
on
0 Posts
So if I cant get into the panel or the meter socket, where should I place the #6 wire to the grounding block?
Is it acceptable to connect directly to the ground rod (even though there is already a clamp on there with the GEC)? How about directly to the metallic raceway instead?
Is it acceptable to connect directly to the ground rod (even though there is already a clamp on there with the GEC)? How about directly to the metallic raceway instead?
#6
This may help, the connection can be made directly to the meter socket in fact some sockets have provisions for that,tapped holes,
250.94 Bonding for Other Systems.
An intersystem bonding termination for connecting intersystem bonding conductors required for other systems shall be provided external to enclosures at the service equipment or metering equipment enclosure and at the disconnecting means for any additional buildings or structures. The intersystem bonding termination shall comply with the following:
(1) Be accessible for connection and inspection.
(2) Consist of a set of terminals with the capacity for connection of not less than three intersystem bonding conductors.
(3) Not interfere with opening the enclosure for a service, building or structure disconnecting means, or metering equipment.
(4) At the service equipment, be securely mounted and electrically connected to an enclosure for the service equipment, to the meter enclosure, or to an exposed nonflexible metallic service raceway, or be mounted at one of these enclosures and be connected to the enclosure or to the grounding electrode conductor with a minimum 6 AWG copper conductor
(5) At the disconnecting means for a building or structure, be securely mounted and electrically connected to the metallic enclosure for the building or structure disconnecting means, or be mounted at the disconnecting means and be connected to the metallic enclosure or to the grounding electrode conductor with a minimum 6 AWG copper conductor.
(6) The terminals shall be listed as grounding and bonding equipment.
250.94 Bonding for Other Systems.
An intersystem bonding termination for connecting intersystem bonding conductors required for other systems shall be provided external to enclosures at the service equipment or metering equipment enclosure and at the disconnecting means for any additional buildings or structures. The intersystem bonding termination shall comply with the following:
(1) Be accessible for connection and inspection.
(2) Consist of a set of terminals with the capacity for connection of not less than three intersystem bonding conductors.
(3) Not interfere with opening the enclosure for a service, building or structure disconnecting means, or metering equipment.
(4) At the service equipment, be securely mounted and electrically connected to an enclosure for the service equipment, to the meter enclosure, or to an exposed nonflexible metallic service raceway, or be mounted at one of these enclosures and be connected to the enclosure or to the grounding electrode conductor with a minimum 6 AWG copper conductor
(5) At the disconnecting means for a building or structure, be securely mounted and electrically connected to the metallic enclosure for the building or structure disconnecting means, or be mounted at the disconnecting means and be connected to the metallic enclosure or to the grounding electrode conductor with a minimum 6 AWG copper conductor.
(6) The terminals shall be listed as grounding and bonding equipment.
#7
The top of the rod should be flush or below the surface.
The bonding terminals should have spaces for all the systems.
The bonding terminals should have spaces for all the systems.
#8
I should have clarified, the conductor is run in 1/2 rmc hence I would have to clamp to rod itself.