Best way to run this wiring

EXISTING CONDITIONS:

From the utility room I have a main panel and it has two PVC conduits that runs down, then exit the 8" concrete block wall, the 3/4" conduit runs about 35' underground to a shed where the washing machine and dryer are. This conduit right now has six individual conductors in it, four #10 and two #12 stranded conductors for the dryer and washer. The 1/2" PVC conduit is abandoned, has nothing in it.

Here are some pictures to make it easier to visualize.





I would like to add a small 1000W gallon water heater in the shed for the washer which would need another 15A circuit. To do that all I really should need is another #12 conductor, I can share the neutral with the washer by putting the two breakers on opposite legs. However, the 3/4" seems too congested to even try.

On top of that, I have in my garage, sitting and collecting dust, five 10' long 1.5" PVC electric conduits. Also collecting dust a coil of NM 6-3 about 60' long. and also about half a dozen of 60A breakers.

So I am thinking, why not dig a new trench, and run a new 1.5" conduit to the shed? I already have the conduits, I already have the breakers, I already have the wires. Run the #6 to the shed and put in a 60A subpanel, and from there, washer, dryer, water heater.

The issue I see is, I don't have the room (as you can see from the picture), to run a 1.5" conduit from the panel through the concrete wall, the wall is very close to the door, and I have other pipes in the way. So I am thinking to reuse the existing 3/4" and 1/2" as pictured above.

Basically, it means on the outside of the wall, I would like a weatherproof (most likely PVC) box, that I would mount onto the wall where the two pipes currently exit. The two existing PVC conduits would tie in on the back side, then from there, I would connect to the 1.5" PVC pipe at the bottom then run underground for 35'. The only thing in the 1.5" conduit is the 6-3 NM cable. But in the future, I can add more wiring if necessary. Does that sound reasonable? Something like this?



I can't find any weatherproof junction box that has a 1.5" KO at the bottom, and two 3/4" KO holes on the back. Does this mean I will need to get a deep box and drill my own KO holes? Or is there a better way?
 
Sponsored Links
  #2  
Old 08-07-15, 09:02 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,515
The 3/4" conduit you have is big enough to contain (3) #6 THHN (black,red,white) + (1) #10 THHN (green) conductor -- enough for up to a 70A subpanel in the shed. If you use #8 THHN, up to 50A. The shed should already have a subpanel as code allows for only one feed per building, and the shed already has two.

It should be a simple job of adding a panel on the shed side, and using the old wires to pull through new wires. A ground rod will need to be added at the shed and bonded to the ground bar with #6 copper.

The NM cannot be used underground.
 
  #3  
Old 08-07-15, 09:21 AM
Member
Thread Starter
Join Date: Oct 2005
Location: Florida
Posts: 1,466
You mean I cannot feed the NM through the 1.5" conduit buried underground but I can do so with individual conductors?

There is no subpanel in the shed now. Well, I don't know if it's shed technically, it's probably more like a "lean to". It's not standalone.
 
  #4  
Old 08-07-15, 09:28 AM
Member
Thread Starter
Join Date: Oct 2005
Location: Florida
Posts: 1,466
Never mind. I just saw a reference that says you can't run NM cable in outdoor conduits, buried or not. So I guess that's out.
 
  #5  
Old 08-07-15, 09:29 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,515
Correct. NM is for indoor, dry locations only.

Outdoors requires either UF (underground feeder) cable, which is very sitff and difficult to using in conduit, or THHN/THWN individual conductors which are rated as waterproof (the W in THWN).

By not standalone, do you mean it's part of the house?
 
  #6  
Old 08-07-15, 09:32 AM
Group Moderator
Join Date: Oct 2004
Location: WI/MN
Posts: 18,761
NM is not allowed outside at all and that includes underground.

Edit: Looks like Ben is faster than me....
 
  #7  
Old 08-07-15, 09:46 AM
Member
Thread Starter
Join Date: Oct 2005
Location: Florida
Posts: 1,466
"By not standalone, do you mean it's part of the house?"

It's a lean-to shed. Meaning there is no "back wall" or the back is actually the exterior wall of the house. Something like this.



It is not a standalone structure 40' away from the main house. I don't know if you call it a "separate building".
 
  #8  
Old 08-07-15, 09:53 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,515
I think it's fair to call this part of the house. Meaning you can run as many circuits as you want to this area from the main panel without a subpanel being required. If it is more convenient to do so, you could install a panel here. To address the immediate need with the least cost, reusing the abandoned 1/2" conduit with #14 THHN in black, white, green would be adequate for the 1000W heater.
 
  #9  
Old 08-07-15, 11:57 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,595
I would look at relocation of the laundry room. I would not want to take the clothes outside to wash them.
 
  #10  
Old 08-07-15, 01:12 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,515
I might not mind if my back yard had that kind of weather.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes